A 10 kVA, 400/200 V, 1-phase transformer with 2% resistance and 2% leakage reactance. It draws steady short circuit current at angle of
  • a)
    45°
  • b)
    75°
  • c)
    135°
  • d)
Correct answer is option 'A'. Can you explain this answer?

Mihir Khanna answered
Given Data:
  • Transformer Rating: 10 kVA, 400/200 V, 1-phase
  • Resistance (R): 2%
  • Leakage Reactance (X): 2%
Steps to Calculate the Angle of Short-Circuit Current:
  1. Determine the Impedance: The impedance ZZZ of the transformer can be calculated using the given percentage values for resistance and reactance:
    Z=R+jXZ = R + jXZ=R+jX
    where RRR and XXX are the resistance and reactance.
    Given:
    R=2% of Z (assuming Z as base impedance, Z = 100)R = 2\% \text{ of } Z \text{ (assuming Z as base impedance, Z = 100)}R=2% of Z (assuming Z as base impedance, Z = 100) X=2% of Z (assuming Z as base impedance, Z = 100)X = 2\% \text{ of } Z \text{ (assuming Z as base impedance, Z = 100)}X=2% of Z (assuming Z as base impedance, Z = 100)
  2. Calculate the Impedance Angle: The impedance angle θ\thetaθ is determined by:
    θ=tan⁡−1(XR)\theta = \tan^{-1} \left(\frac{X}{R}\right)θ=tan−1(RX​)
    Substituting R=2R = 2R=2 and X=2X = 2X=2:
    θ=tan⁡−1(22)=tan⁡−1(1)=45°\theta = \tan^{-1} \left(\frac{2}{2}\right) = \tan^{-1}(1) = 45°θ=tan−1(22​)=tan−1(1)=45°
Angle of the Short-Circuit Current:
The angle of the short-circuit current is equal to the angle of the impedance because the current in a short-circuit condition is essentially the same as the impedance angle.
Conclusion:
The steady short-circuit current draws at an angle of:
1. 45°

While conducting open circuit test and short circuit test on a transformer, status of low-voltage and high-voltage windings will be such that in
  • a)
    OC test – l.v. open, SC test-h.v. short-circuited
  • b)
    OC test – h.v. open, SC test-l.v. short-circuited
  • c)
    OC test – l.v. open, SC test-l.v. short-circuited
  • d)
    OC test – h.v. open, SC test-h.v. short-circuited
Correct answer is option 'A'. Can you explain this answer?

For transformer testing:
  • Open Circuit (OC) Test:
    • This test is used to determine the core losses and no-load characteristics of the transformer. In this test, the high-voltage (HV) winding is energized, and the low-voltage (LV) winding is kept open.
  • Short Circuit (SC) Test:
    • This test is used to measure the copper losses and the impedance of the transformer. In this test, the low-voltage (LV) winding is short-circuited, and the high-voltage (HV) winding is energized.
So, the correct configuration is:
2. OC test – l.v. open, SC test – h.v. short-circuited

For given applied voltage, with the increase in frequency of the applied voltage
  • a)
    eddy current loss will decrease
  • b)
    eddy current loss will increase
  • c)
    eddy current loss will remain unchanged
  • d)
    none of the above
Correct answer is option 'C'. Can you explain this answer?

Partho Saha answered
Explanation:
Eddy currents are produced in a conductor when it is exposed to a changing magnetic field. These currents flow in closed loops and generate heat, which can cause energy losses. The amount of eddy current loss depends on various factors such as the material properties of the conductor, the frequency of the applied voltage, and the shape of the conductor.

Effect of frequency on eddy current loss:
When a conductor is exposed to an alternating voltage, the frequency of the voltage determines the rate at which the magnetic field changes. Therefore, the frequency of the applied voltage has a significant impact on the amount of eddy current loss in the conductor. The following points explain the effect of frequency on eddy current loss:

- At low frequencies, the magnetic field changes slowly, and eddy currents have enough time to build up and flow through the conductor. As a result, eddy current loss is high at low frequencies.
- At high frequencies, the magnetic field changes rapidly, and eddy currents do not have enough time to build up and flow through the conductor. Therefore, eddy current loss is low at high frequencies.
- At a certain frequency, called the skin depth frequency, the eddy currents are mostly confined to the surface layer of the conductor. This is because the skin depth, which is the depth at which the eddy current density has decreased to 1/e (about 37%) of its surface value, becomes smaller than the thickness of the conductor. At this frequency, the eddy current loss is minimum. The skin depth frequency depends on the material properties of the conductor and the frequency of the applied voltage.

Conclusion:
In conclusion, the eddy current loss in a conductor remains unchanged with the increase in frequency of the applied voltage, provided the skin depth frequency is not reached. Beyond the skin depth frequency, the eddy current loss decreases with an increase in frequency. Thus, the correct option is C.

The size of a transformer core will depend on
  • a)
    frequency
  • b)
    area of the core
  • c)
    flux density of the core material
  • d)
    (A) and (B) both
Correct answer is option 'D'. Can you explain this answer?

Shyamala M answered
For a given transformer rating, as the frequency increases the product of window area and cross sectional area of the limb decreases; which means the iron required for the core decreases. Therefore as the frequency increases, the transformer becomes lighter and smaller in size.
The area of the window and cross sectional area of the limb are the main dimensions of a transformer, the product of which is directly proportional to the size and weight of the transformer. More the product (area), bigger and heavier is the transformer.

If a 2200/220 V, 60 Hz single phase transformer has primary and secondary resistance of 100 Ω and 10 Ω, respectively. Then the value of equivalent resistance of the transformer referred to the primary side and secondary side are
  • a)
    1100 Ω and 20 Ω respectively
  • b)
    20 Ω and 1100 Ω respectively
  • c)
    1100 Ω and 11 Ω respectively
  • d)
    11 Ω and 1100 Ω respectively
Correct answer is option 'C'. Can you explain this answer?

EduRev GATE answered
Concept:
In a transformer, the turns ratio is given by
Where V1 is the primary voltage
V2 is the secondary voltage
N1 is the primary turns
N2 is the secondary turns
I1 is the primary current
Iis the secondary current
The equivalent resistance of the transformer referred to the primary side = R1 + n2R2
The equivalent resistance of the transformer referred to the secondary side = R2 + R1/n2
Calculation:
Given that, primary voltage (V1) = 2200 V
Secondary voltage (V2) = 220 V
Primary resistance (R1) =100 Ω
Secondary resistance (R2) = 10 Ω
Turns ratio = 2200/220 = 10
∴ Equivalent resistance of the transformer referred to the primary side
=> R1 + n2R2 = [100 + (10)2 × 10] = 1100 Ω
∴ Equivalent resistance of the transformer referred to the secondary side
=> R2 + R1/n2 = [10 + 100/(10)2] = 11 Ω

The changes in volume of transformer cooling oil due to variation of atmospheric tem-perature during day and night is taken care of by which part of transformer
  • a)
    Conservator
  • b)
    Breather
  • c)
    Bushings
  • d)
    Buchholz relay
Correct answer is option 'A'. Can you explain this answer?

Rajesh Verma answered
Transformer Cooling Oil and Atmospheric Temperature Changes

Transformer cooling oil is essential in maintaining the optimal temperature of a transformer. During the day and night, the atmospheric temperature changes, which can affect the volume of transformer cooling oil. The changes in volume of transformer cooling oil due to variation of atmospheric temperature during day and night is taken care of by the conservator.

Conservator

A conservator is a cylindrical metal container that connects to the transformer tank. It contains a diaphragm that separates the oil from the air, preventing air from coming into contact with the oil. The conservator acts as a reservoir for the cooling oil, allowing for the expansion and contraction of the oil due to temperature changes.

Working of Conservator

When the atmospheric temperature increases, the volume of the transformer cooling oil expands, causing the oil level in the conservator to rise. The oil flows from the transformer tank to the conservator, and the diaphragm in the conservator expands to accommodate the increased volume of oil. In contrast, when the atmospheric temperature decreases, the volume of the transformer cooling oil contracts, causing the oil level in the conservator to drop. The oil flows from the conservator to the transformer tank, and the diaphragm in the conservator contracts to accommodate the decreased volume of oil.

Conclusion

In conclusion, the changes in volume of transformer cooling oil due to variation of atmospheric temperature during day and night is taken care of by the conservator. The conservator acts as a reservoir for the cooling oil, allowing for the expansion and contraction of the oil due to temperature changes.

Part of the transformer which is most subject to damage from overheating is
  • a)
    iron core
  • b)
    copper winding
  • c)
    winding insulation
  • d)
    frame or case
Correct answer is option 'C'. Can you explain this answer?

As insulation is placed over the winding,when transformer subject to overheating due to supplied a more load.the insulation may damages than winding.

The efficiency of a 20 KVA, 2000/200 V, single phase transformer at unity pf is 98%. The total losses at this condition is?
  • a)
    408W
  • b)
    4.08kW
  • c)
    204W
  • d)
    2.04kW
Correct answer is option 'A'. Can you explain this answer?



Given data:
- Power rating of the transformer (S) = 20 kVA
- Voltage rating of the transformer (V1/V2) = 2000/200 V
- Efficiency (η) = 98%

Calculating total losses:
- Efficiency (η) = Output power / Input power
- Input power = Output power / Efficiency
- Input power = 20 kVA / 0.98 = 20.41 kVA
- Input power = 20.41 kW

Calculating copper losses:
- Copper losses = Input power - Output power
- Copper losses = 20.41 kW - 20 kVA = 0.41 kW = 410 W

Calculating iron losses:
- Iron losses = Total losses - Copper losses
- Iron losses = 20.41 kW - 410 W = 20 kW

Answer:
- The total losses at this condition is 410 W. Therefore, the correct option is (a) 408 W.

A one-phase, 50 Hz, 40 kVA transformer with a ratio of 2000 V/250 V has a primary resistance of 1.15 Ω and a secondary resistance of 0.0155 Ω. Calculate total copper loss on half of the full load. 
  • a)
    856.8 W
  • b)
    214.2 W
  • c)
    642.6 W
  • d)
    428.4 W
Correct answer is option 'B'. Can you explain this answer?

Vibhor Goyal answered
Concept:
Consider a two winding single phase transformer as shown below,
N1 = primary winding turns
N2 = secondary winding turns
V1 = primary winding voltage
V2 = secondary winding voltage
I1 = current through the primary winding
I2 = current through the secondary winding
Transformation ratio: It is defined as the ratio of the secondary voltage to the primary voltage. It is denoted by K.
Transformer equivalent circuit with respect to secondary can be represented a show below
Where R02 = Effective resistance of the transformer as referred to the secondary side of the transformer.
R02 = R2 + R1'    ------- (2)
R1' = Equivalent primary resistance as referred to the secondary winding
R1' = R× K 2  ------ (3)
Similarly, effective resistance of the transformer as referred to the primary side of the transformer is given as,
R01 = R1 + R2
R2' = Equivalent secondary resistance as referred to the primary winding
R2' = R2 / K 2
Calculation:
Given data
V1 = 2000 V, V2 = 250 V, R1 = 1.15 Ω, R2 = 0.0155 Ω
From equation(1)
K= V2 / V1
K = 250 / 2000
K = 1 / 8
Effective resistance of the transformer as referred to the secondary of the transformer.
From equations(2) & (3)
R02 = 0.0155 + 1.15 / 82
R02 = 0.0335 Ω
Power output P = 40 kVA
V2 I= 40 × 103
I2 = 40000 / 250
I2 = 160 A = Ifl
Ifl is the full load current flowing through the secondary.
We required to find power loss at half full load condition
So, current at half full load is given as,
∴ Total power loss at half full load condition is given as,
Phfl = I2hfl × R02
Phfl = 802 × 0.0335
Phfl = 214.2 W

In a transformer, the load current is kept constant, while the power factor is varied. Under this situation, zero voltage regulation will be observed
  • a)
    independent of load power factor
  • b)
    load power factor is leading
  • c)
    load power factor is lagging
  • d)
    at power factor equal to unity
Correct answer is option 'B'. Can you explain this answer?

Engineers Adda answered
Voltage regulation is the change in secondary terminal voltage from no load to full load at a specific power factor of load and the change is expressed in percentage.
E2 = no-load secondary voltage
V2 = full load secondary voltage
Voltage regulation for the transformer is given by the ratio of change in secondary terminal voltage from no load to full load to no load secondary voltage.

+ sign is used for lagging loads and
- ve sign is used for leading loads
Hence voltage regulation can be negative only for capacitive loads
In transformer minimum voltage regulation occurs when the power factor of the load is leading.
The voltage regulation of the transformer is zero at a leading power factor load such as a capacitive load.
For zero voltage regulation, E2 = V2
> IR cos φ = IX sin φ (negative sign represents leading power factor loads)

This is the leading power factor at which voltage regulation becomes zero while supplying the load.

The value of flux involved m the e.m.f. equation of a transformer is
  • a)
    average value
  • b)
    r.m.s. value
  • c)
    maximum value
  • d)
    instantaneous value
Correct answer is option 'C'. Can you explain this answer?

Swati Shah answered
The value of flux involved in the e.m.f. equation of a transformer is the maximum value. Here's why:

Explanation:
- The e.m.f. equation of a transformer is given by E = 4.44fφN, where E is the induced e.m.f., f is the frequency of the alternating current, φ is the maximum value of the flux, and N is the number of turns in the winding.
- The maximum value of the flux is the peak value of the sinusoidal waveform of the flux. This is because the e.m.f. induced in the winding of the transformer is proportional to the rate of change of flux, and the maximum rate of change occurs when the flux is changing from its maximum to its minimum value.
- The average value of the flux is zero, since the flux waveform is symmetrical about the zero axis.
- The r.m.s. value of the flux is given by the square root of the mean square value of the waveform, which is √(1/2φ²). This value is not relevant to the e.m.f. equation of a transformer.
- The instantaneous value of the flux is constantly changing, and is not a useful value to consider for the e.m.f. equation of a transformer.

Conclusion:
Therefore, the value of flux involved in the e.m.f. equation of a transformer is the maximum value.

Which of the following informations are obtained from short-circuit test?
I. Ohmic losses at rated current
II. Equivalent resistance and leakage reactance
III. Core losses
IV. Voltage regulation
  • a)
    I, II, IV
  • b)
    II, III
  • c)
    I, II, III
  • d)
    II, III, IV
Correct answer is option 'A'. Can you explain this answer?

Sanaya Basu answered


Short-Circuit Test Information


  • Ohmic losses at rated current: The short-circuit test provides information about the ohmic losses that occur in the transformer windings when they are subjected to rated current.

  • Equivalent resistance and leakage reactance: By performing the short-circuit test, the equivalent resistance and leakage reactance of the transformer can be determined. This information is crucial for understanding the transformer's impedance characteristics.

  • Core losses: The core losses of the transformer can also be estimated from the short-circuit test results. This helps in assessing the overall efficiency of the transformer.

  • Voltage regulation: The short-circuit test data can be used to calculate the voltage regulation of the transformer. Voltage regulation is an important parameter that indicates how well the transformer can maintain a constant output voltage under varying load conditions.



In conclusion, the short-circuit test provides valuable information related to ohmic losses, equivalent resistance, leakage reactance, core losses, and voltage regulation of a transformer. This data is essential for analyzing the performance and efficiency of the transformer in practical applications.

If the supply frequency to the transformer is increased, the iron loss will
  • a)
    not change
  • b)
    decrease
  • c)
    increase
  • d)
    any of the above
Correct answer is option 'C'. Can you explain this answer?

Sparsh Saini answered
As frequency increases, the flux density in the core decreases but as the iron loss is directly proportional to the frequency hence effect of increased frequency will be reflected in increase of the iron losses.

A 4000 V/2000 V, 60 Hz single phase transformer has a total impedance of 60 Ω referred to the primary side. The primary and secondary windings have negligible resistances. If the transformer supplies a resistive of 20 Ω, the full load voltage at the secondary side will be
  • a)
    1143 V
  • b)
    1600 V
  • c)
    2000 V
  • d)
    3200 V
Correct answer is option 'A'. Can you explain this answer?

Concept:
Consider a two winding single phase transformer as shown below,
N1 = primary winding turns
N2 = secondary winding turns
V1 = primary winding voltage
V2 = secondary winding voltage
I1 = current through the primary winding
I2 = current through the secondary winding
Transformation ratio: It is defined as the ratio of the secondary voltage to the primary voltage. It is denoted by k.
K=N2N1=V2V1=I1I2" tabindex="0">K=N2N1=V2V1=I1I----- (1)Transformer equivalent circuit with respect to secondary can be represented a show below
Where R02 = Effective resistance referred to the secondary side of the transformer.
R02 = R2 + R1' ........ (2)
R1' = Primary winding resistance as referred to the secondary side.
R1' = R1 × k2 ......... (3)
Similarly, the effective resistance referred to the primary side of the transformer is given as,
R01 = R1 + R2' 
R2' = Secondary winding resistance as referred to the primary side.
R2' = R2 / k2
Calculation:
 
Given total impedance of the transformer referred to primary R01 = 60 Ω 
Transformation ratio k = V2 / V1 = 2000 / 4000 = 0.5
Total impedance of the transformer referred to secondary when primary and secondary windings have negligible resistances is given as
R02 = R01 × k2
= 60 / 4 = 15 Ω
Apply the voltage division rule to find voltage across the load
VL = 2000 × 20 / (15 + 20)
VL = 1143 V

The single phase converter has a full load secondary current of 200 A, while the primary current is one-tenth of this value. Its primary resistance and secondary winding resistances are 1.5 Ω and 0.015 Ω, respectively. The leakage reactance values of the primary and secondary windings are 2 Ω and 0.02 Ω respectively. Which primary voltage will transmit the full load current through a short-circuit secondary, not neglecting the load current?
  • a)
    80 V
  • b)
    120 V
  • c)
    100 V
  • d)
    40 V
Correct answer is option 'C'. Can you explain this answer?

Crack Gate answered
Calculation:
Given:
Primary resistance of Transformer R1 = 1.5 Ω
The primary reactance of Transformer X1 = 2j Ω
Secondary resistance of Transformer R2 = 0.015 Ω
Secondary reactance of Transformer X2 = 0.02j Ω
Primary Current I1 = 20 A
Secondary Current I2 = 200 A
Let Primary Induced Emf and Secondary Induced Emf be E1 and E2
Let primary Voltage be V1
Circuit Diagram Shown:
E2 = 200 (0.015 + j0.02)
E= 5∠ 53.13
Turns ratio (N) is given by
Now, by Applying KCL in Primary Circuit

The magnetisation branch of an equivalent circuit of a transformer is drawn in ________ with supply voltage.
  • a)
    both series and parallel
  • b)
    series only
  • c)
    parallel only
  • d)
    Neither series nor parallel
Correct answer is option 'C'. Can you explain this answer?

Concept:
The equivalent circuit of the transformer is
I1 = Primary winding current
I2 ' =Secondary winding current referred to the primary side
I= NO - load current
I= Core loss component
I= magnetizing component No-load current is almost the same when we apply the load also.
The magnetizing branch circuit is connected in parallel to the supply voltage as the No-load current is constant while we apply load also. Therefore Core loss is also constant as Iremains constant

Which of the statements made here are incorrect regarding the transformer?
I. Maximum voltage regulation occurs at the leading p.f.
II. Maximum voltage regulation occurs when load p.f. angle and impedance angle of the leakage impedance are same.
III. V.R. at zero p.f. is always zero.
IV. V.R. of a transformer may be negative at leading p.f.
  • a)
    I, II, III
  • b)
    IV
  • c)
    I, III
  • d)
    I, IV, III
Correct answer is option 'B'. Can you explain this answer?

Prasad Saini answered
Incorrect Statements Regarding the Transformer

There are four statements given regarding the transformer, and we need to identify which of them are incorrect. Let's analyze each statement one by one.

I. Maximum voltage regulation occurs at the leading p.f.
This statement is incorrect. Voltage regulation refers to the change in output voltage of a transformer when the load varies. The maximum voltage regulation occurs at the lagging power factor, not at the leading power factor. This is because at lagging power factor, the load current lags behind the voltage, resulting in a higher drop across the impedance of the transformer.

II. Maximum voltage regulation occurs when load p.f. angle and impedance angle of the leakage impedance are the same.
This statement is incorrect. The voltage regulation of a transformer depends on the power factor angle difference between the load and the transformer impedance. The maximum voltage regulation occurs when the load power factor angle is equal to the angle between the impedance of the transformer and the voltage. In other words, the maximum voltage regulation occurs when the load power factor angle is equal to the angle of the impedance voltage drop in the transformer.

III. V.R. at zero p.f. is always zero.
This statement is incorrect. The voltage regulation at zero power factor is not always zero. Zero power factor means that the load is purely reactive, and in this case, the voltage regulation can be significant. The reactive power causes additional losses in the transformer, resulting in a voltage drop.

IV. V.R. of a transformer may be negative at the leading p.f.
This statement is correct. The voltage regulation of a transformer can be negative at the leading power factor. Negative voltage regulation means that the output voltage of the transformer increases as the load increases. This can occur when the load power factor angle is leading and the impedance angle of the transformer is lagging.

Conclusion
Based on the analysis above, the incorrect statements regarding the transformer are:
I. Maximum voltage regulation occurs at the leading p.f.
II. Maximum voltage regulation occurs when load p.f. angle and impedance angle of the leakage impedance are the same.
III. V.R. at zero p.f. is always zero.

Therefore, the correct answer is option 'B', i.e., IV.

Which of the following is the correct mathematical relationship that connects primary and secondary parameters of a transformer?
  • a)
    (V2 / V1) = (N1 / N2) = (I1 / I2) = k
  • b)
    (V2 / V1) = (N2 / N1) = (I2 / I1) = k
  • c)
    (V/ V1) = (N2 / N1) = (I1 / I2) = k
  • d)
    (V2 / V1) = (N1 / N2) = (I2 / I1) = k
Correct answer is option 'C'. Can you explain this answer?

Sushant Mehta answered

Mathematical Relationship between Primary and Secondary Parameters of a Transformer

Transformer parameters are interconnected through a set of equations that relate primary and secondary values. The correct mathematical relationship is expressed as:

(V2 / V1) = (N2 / N1) = (I1 / I2) = k

Explanation:
- V2 / V1: Ratio of secondary voltage to primary voltage remains constant and is equal to the turns ratio of the transformer.
- N2 / N1: Ratio of secondary turns to primary turns is constant, indicating the turns ratio.
- I1 / I2: Ratio of primary current to secondary current is also constant and is inversely proportional to the turns ratio.
- k: Represents the transformation ratio, which remains constant for a given transformer.

This relationship is crucial in understanding the behavior of transformers and is utilized in various calculations and applications in electrical engineering. It helps in determining the voltage, current, and turns ratio between primary and secondary sides of the transformer, enabling efficient power transfer and voltage transformations.

For matching a circuit of output impedance 200 ohms with a load of 8 ohms, the turns ratio of the two winding of transformer should be
  • a)
    25
  • b)
    1/25
  • c)
    1/5
  • d)
    5
Correct answer is option 'D'. Can you explain this answer?

Crack Gate answered
Concept:
Transformers are used for impedance matching applications. This is explained with the help of the following figure:
The load impedance reflected on the primary side is redrawn as shown:
For the load to match with the source resistance:
Calculation:
With RL = 8 Ω, and RS = 200 Ω, the transformation ratio will be:

Chapter doubts & questions for Single-Phase Transformers - Electrical Machines for Electrical Engg. 2026 is part of Electrical Engineering (EE) exam preparation. The chapters have been prepared according to the Electrical Engineering (EE) exam syllabus. The Chapter doubts & questions, notes, tests & MCQs are made for Electrical Engineering (EE) 2026 Exam. Find important definitions, questions, notes, meanings, examples, exercises, MCQs and online tests here.

Chapter doubts & questions of Single-Phase Transformers - Electrical Machines for Electrical Engg. in English & Hindi are available as part of Electrical Engineering (EE) exam. Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.

Top Courses Electrical Engineering (EE)