In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)
  • a)
    0.0329 kg/s
  • b)
    0.0435 kg/s
  • c)
    0.0588 kg/s
  • d)
    0.0689 kg/s
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
In aqua ammonia absorption system the heat is supplied to generator by...

View all questions of this test
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer?
Question Description
In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer?.
Solutions for In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer?, a detailed solution for In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? has been provided alongside types of In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In aqua ammonia absorption system the heat is supplied to generator by condensing steam at 0.2 MPa and 90% dryness fraction. The temperature to be maintained in refrigeration is –10°C and the ambient temperature is 30°C. The actual COP is the 40% of the maximum COP and the refrigeration effect is 20 TR. The required flow rate will be (Given: at 0.2 MPa saturation, temperature = 120.2°C = 2201.9 kJ/kg)a)0.0329 kg/sb)0.0435 kg/sc)0.0588 kg/sd)0.0689 kg/sCorrect answer is option 'C'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev