Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  The emf per turn of a single phase 10 kVA, 22... Start Learning for Free
The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T is
  • a)
    300 cm2    
  • b)
    200 cm2
  • c)
    100 cm2    
  • d)
    25 cm2
Correct answer is option 'A'. Can you explain this answer?
Verified Answer
The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transform...
Maximum flux,

∴ New cross-sectional area of core,
View all questions of this test
Most Upvoted Answer
The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transform...
Solution:

Given data:

EMF per turn, E = 10 V
Single-phase transformer rating, S = 10 kVA
Primary voltage, V1 = 2200 V
Secondary voltage, V2 = 220 V
Frequency, f = 50 Hz
Maximum flux density, Bm = 1.5 T

1. Calculation of the number of turns:

The EMF per turn of the transformer is given as 10 V. Therefore, the total number of turns required on the transformer can be calculated as:

E = 4.44fΦNT
10 = 4.44 × 50 × Φ × N
N = 10/(4.44 × 50 × Φ)
N = 225/Φ

2. Calculation of the flux density:

The flux density of the transformer can be calculated as:

V1/N1 = V2/N2
2200/N1 = 220/N2
N1/N2 = 10
Φ = Bm × A
Bm = Φ/A
Φ = Bm × A = Bm × (2l + 2b)/2
Φ = Bm × (2l + 2b)/2 = Bm × l × b
Bm = Φ/(l × b)
Bm = V1/(4.44fN1A)

3. Calculation of the core area:

The area of the core required for the maximum flux density of 1.5 T can be calculated as:

A = V1/(4.44fN1Bm)
A = 2200/(4.44 × 50 × 225/Φ × 1.5)
A = 300 cm2

Therefore, the correct option is A) 300 cm2.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Question Description
The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? for Electrical Engineering (EE) 2025 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer?.
Solutions for The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer?, a detailed solution for The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? has been provided alongside types of The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The emf per turn of a single phase 10 kVA, 2200/220 V, 50 Hz transformer is 10 V. The net cross-sectional area of core for a maximum flux density of 1.5 T isa)300 cm2 b)200 cm2c)100 cm2 d)25 cm2Correct answer is option 'A'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev