SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)
  • a)
    8, 5
  • b)
    9, 5
  • c)
    5, 9
  • d)
    5, 8
Correct answer is option 'C'. Can you explain this answer?
Most Upvoted Answer
SCR with a rating of 1200 V and 250 A are available to be used in a st...
Derating factor = 1 – string efficiency
Free Test
Community Answer
SCR with a rating of 1200 V and 250 A are available to be used in a st...
Given parameters:
SCR rating: 1200 V, 250 A
Required parameters: 8 kV, 1 kA
Derating factor: 0.2

To determine the number of parallel and series units required, we need to consider both the voltage and current ratings of the SCR units.

1. Derating the voltage:
Since the derating factor is 0.2, the maximum allowable voltage for each SCR unit can be calculated as follows:
Maximum voltage = Rated voltage - (Rated voltage * Derating factor)
Maximum voltage = 1200 V - (1200 V * 0.2) = 960 V

To handle 8 kV, we need to determine the number of series units required:
Number of series units = Required voltage / Maximum voltage
Number of series units = 8000 V / 960 V = 8.33 ≈ 9 (rounded up to the nearest whole number)

2. Derating the current:
Since the derating factor is 0.2, the maximum allowable current for each SCR unit can be calculated as follows:
Maximum current = Rated current - (Rated current * Derating factor)
Maximum current = 250 A - (250 A * 0.2) = 200 A

To handle 1 kA, we need to determine the number of parallel units required:
Number of parallel units = Required current / Maximum current
Number of parallel units = 1000 A / 200 A = 5

Therefore, the number of parallel and series units required are respectively 5 and 9.

Hence, the correct answer is option C) 5, 9.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer?
Question Description
SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer?.
Solutions for SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer?, a detailed solution for SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? has been provided alongside types of SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice SCR with a rating of 1200 V and 250 A are available to be used in a string to handle 8 kV and 1kA. The number of parallel and series units required are respectively _____ (Take derating factor is 0.2)a)8, 5b)9, 5c)5, 9d)5, 8Correct answer is option 'C'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev