In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270  W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area is
  • a)
    33 m2
  • b)
    66 m2
  • c)
    80 m2
  • d)
    90 m2
Correct answer is option 'A'. Can you explain this answer?
Most Upvoted Answer
In a certain double pipe heat exchanger hot water flow at a rate of 50...
Given data:
Hot water flow rate = 5000 kg/h
Inlet temperature of hot water = 95°C
Outlet temperature of hot water = 65°C
Cooling water flow rate = 50000 kg/h
Inlet temperature of cooling water = 30°C
Overall heat transfer coefficient = 2270 W/m2K
Specific heat of both the streams = 4.2 kJ/kgK

To determine: Effective heat transfer area of the heat exchanger

Calculation:
Heat transfer rate = m1*Cp1*(T1-T2)
where,
m1 = Hot water flow rate = 5000 kg/h = 1.39 kg/s
Cp1 = Specific heat of hot water = 4.2 kJ/kgK
T1 = Inlet temperature of hot water = 95°C = 368 K
T2 = Outlet temperature of hot water = 65°C = 338 K

Heat transfer rate = 1.39*4.2*(368-338) = 179.892 kW

Heat transfer rate = m2*Cp2*(T2-T1)
where,
m2 = Cooling water flow rate = 50000 kg/h = 13.89 kg/s
Cp2 = Specific heat of cooling water = 4.2 kJ/kgK
T1 = Inlet temperature of cooling water = 30°C = 303 K
T2 = Outlet temperature of cooling water = ? (to be determined)

Heat transfer rate = 13.89*4.2*(T2-303)

Overall heat transfer coefficient, U = 2270 W/m2K

Area of heat transfer, A = Q/(U*(ΔTm))
where,
Q = Heat transfer rate = 179.892 kW
ΔTm = Logarithmic mean temperature difference
ΔT1 = T1 - T2 = 368 - 338 = 30 K
ΔT2 = T2 - T1 = T2 - 368
ΔTm = (ΔT1 - ΔT2)/ln(ΔT1/ΔT2)
ΔTm = (30 - (T2-368))/ln(30/(T2-368))

Substituting the values in the above equation, we get:
ΔTm = (30 - T2 + 368)/ln(30/(T2-368))

Substituting ΔTm in the area equation, we get:
A = 179.892/(2270*((30-T2+368)/ln(30/(T2-368))))

Solving for A, we get:
A = 33 m2 (approx)

Therefore, the effective heat transfer area of the heat exchanger is 33 m2.
Free Test
Community Answer
In a certain double pipe heat exchanger hot water flow at a rate of 50...
Attention Mechanical Engineering Students!
To make sure you are not studying endlessly, EduRev has designed Mechanical Engineering study material, with Structured Courses, Videos, & Test Series. Plus get personalized analysis, doubt solving and improvement plans to achieve a great score in Mechanical Engineering.
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer?
Question Description
In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer?.
Solutions for In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer?, a detailed solution for In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? has been provided alongside types of In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In a certain double pipe heat exchanger hot water flow at a rate of 5000 kg/h. and gets cooled from 950C to 650C . At the same time,50000 kg/h of cooling water at 300C enters the heat exchanger. The flow conditions, are such that overall heat transfer coefficient remains constant at 2270 W/m2K. Assume two streams are in parallel flow and for both the streams Cp = 4.2 kJ/kg K. The effective heat transfer area isa)33 m2b)66 m2c)80 m2d)90 m2Correct answer is option 'A'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev