A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COP
  • a)
    374.9 K
  • b)
    380.7 K
  • c)
    388.4 K
  • d)
    418.7 K
Correct answer is option 'A'. Can you explain this answer?
Verified Answer
A vapour absorption refrigeration system works with generator, ambient...

View all questions of this test
Most Upvoted Answer
A vapour absorption refrigeration system works with generator, ambient...
Solution:

Given,
Temperature at generator (Tg) = 360 K
Temperature at ambient (Ta) = 310 K
Temperature at evaporator (Te) = 260 K
New temperature at evaporator (Te') = 250 K
COP of the system is constant (i.e., same)

Formula:
COP = Te / (Tg - Te)

From the above equation,
(Tg - Te) / Te = constant

(Tg - Te)1 / Te1 = (Tg - Te)2 / Te2 (where 1 represents initial conditions and 2 represents final conditions)

Now, we need to find Tg2 such that COP remains the same.

(Tg2 - Te2) / Te2 = (Tg1 - Te1) / Te1

(Tg2 - 250) / 250 = (360 - 260) / 260

Tg2 = 374.9 K

Therefore, the generator temperature should be 374.9 K in order to operate the system with the same COP when the evaporator temperature falls to 250 K.
Attention Mechanical Engineering Students!
To make sure you are not studying endlessly, EduRev has designed Mechanical Engineering study material, with Structured Courses, Videos, & Test Series. Plus get personalized analysis, doubt solving and improvement plans to achieve a great score in Mechanical Engineering.
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer?
Question Description
A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer?.
Solutions for A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A vapour absorption refrigeration system works with generator, ambient and evaporator temperature as 360 K, 310 K and 260 K respectively. If the evaporator temperature falls to 250 K what should be the generator temperature in order to operate the system with same COPa)374.9 Kb)380.7 Kc)388.4 Kd)418.7 KCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev