Mechanical Engineering Exam  >  Mechanical Engineering Questions  >  Common data for 12 & 13A commercial refri... Start Learning for Free
Common data for 12 & 13
A commercial refrigerator is used to keep the refrigerated space at -300C by rejecting its waste heat to cooling water. This cooling water enters the condenser at 180C (hw = 75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94 kJ/kg). The refrigerant enters the condenser at 1.2 MPa, 650C (h = 295.16 kJ/kg) and leaves at 420C (h = 111.23 kJ/kg). The inlet state of the compressor is 60 kPa, -340C (h = 230.03 kJ/kg) and the compressor is estimated to gain a net heat of 450W from the surroundings:
Q. The theoretical maximum refrigeration load for the same power input to the compressor is
  • a)
    21.31 kW
  • b)
    17.17 kW
  • c)
    26.73 kW
  • d)
    12.72 kW
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
Common data for 12 & 13A commercial refrigerator is used to keep t...
View all questions of this test
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer?
Question Description
Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer?.
Solutions for Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Common data for 12 & 13A commercial refrigerator is used to keep the refrigerated space at-300C by rejecting its waste heat tocooling water. This cooling waterenters the condenser at 180C (hw =75.47 kJ/kg) with a rate of 0.25 kg/s and leaves at 260C (hw = 108.94kJ/kg). The refrigerant enters thecondenser at 1.2 MPa, 650C (h =295.16 kJ/kg) and leaves at 420C(h = 111.23 kJ/kg). The inlet stateof the compressor is 60 kPa, -340C(h = 230.03 kJ/kg) and thecompressor is estimated to gain a net heat of 450W from thesurroundings:Q. The theoretical maximumrefrigeration load for the samepower input to the compressor isa)21.31 kWb)17.17 kWc)26.73 kWd)12.72 kWCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.