A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?
  • a)
    3.8 % down
  • b)
    3.8 % up
  • c)
     4.6 % up
  • d)
    4.6 % down
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap...

Hence, voltage to be raised, for maintaining rated voltage = 4.6%.
Thus, tap setting required on the HV side = -4.6% or 4.6 % down.
View all questions of this test
Most Upvoted Answer
A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap...
Phase transformer has a rated voltage ratio of 76.2 kV/33 kV.

The transformer is rated for a power of 50 MVA, which means it can deliver 50 million watts of power at its rated voltage and frequency.

The primary voltage rating of the transformer is 76.2 kV, which is the voltage level at which the transformer is designed to receive power from the power grid.

The secondary voltage rating of the transformer is 33 kV, which is the voltage level at which the transformer is designed to deliver power to the load.

The transformer is a single-phase transformer, which means it can only handle power for one phase of a three-phase power system.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Question Description
A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2025 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer?.
Solutions for A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 50 MVA, 76.2/33 kV, 1-φ, 50 Hz, two-winding transformer with tap changer has percentage impedance of (0.5 + j7.0). What tapping must be used to maintain rated voltage at the secondary on full load at 0.8 lagging power factor?a)3.8 % downb)3.8 % upc)4.6 % upd)4.6 % downCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev