The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero). 
    Correct answer is between '0.1,0.1'. Can you explain this answer?
    Verified Answer
    The positive, negative and zero sequence reactances of a wye-connected...
    View all questions of this test
    Most Upvoted Answer
    The positive, negative and zero sequence reactances of a wye-connected...
    Given data:
    - Positive sequence reactance (X1) = 0.2 pu
    - Negative sequence reactance (X2) = 0.2 pu
    - Zero sequence reactance (X0) = 0.1 pu
    - Terminal voltage (Vt) = 1 pu
    - Fault current (If) = 3.75 pu

    Calculating the minimum inductive reactance:
    To limit the fault current to a desired value, we need to connect an inductive reactance (Xg) between neutral and ground. Let's assume the fault impedance (Zf) is zero.

    Positive sequence fault current:
    The positive sequence fault current (I1f) can be calculated using the following formula:
    I1f = Vt / (X1 + Xg)

    Negative sequence fault current:
    The negative sequence fault current (I2f) can be calculated using the following formula:
    I2f = Vt / (X2 + Xg)

    Zero sequence fault current:
    The zero sequence fault current (I0f) can be calculated using the following formula:
    I0f = Vt / (X0 + Xg)

    Maximum fault current:
    The maximum fault current (If_max) occurs when the fault impedance is zero and all the fault current flows through the positive sequence impedance. It can be calculated as:
    If_max = I1f = Vt / (X1 + Xg)

    Calculating the minimum inductive reactance:
    To limit the fault current to 3.75 pu, we need to ensure that the fault current (If) is less than or equal to 3.75 pu. Therefore,
    If_max = Vt / (X1 + Xg) <=>

    Solving the above equation for Xg, we get:
    Xg >= Vt / 3.75 - X1

    Substituting the given values, we have:
    Xg >= 1 / 3.75 - 0.2
    Xg >= 0.1

    Therefore, the minimum value of the inductive reactance required to be connected between neutral and ground is 0.1 pu.
    Explore Courses for GATE exam
    The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer?
    Question Description
    The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? for GATE 2024 is part of GATE preparation. The Question and answers have been prepared according to the GATE exam syllabus. Information about The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? covers all topics & solutions for GATE 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer?.
    Solutions for The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? in English & in Hindi are available as part of our courses for GATE. Download more important topics, notes, lectures and mock test series for GATE Exam by signing up for free.
    Here you can find the meaning of The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer?, a detailed solution for The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? has been provided alongside types of The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The positive, negative and zero sequence reactances of a wye-connected synchronous generator are 0.2 pu, 0.2 pu, and 0.1 pu, respectively. The generator is on open circuit with a terminal voltage of 1 pu. The minimum value of the inductive reactance, in pu, required to be connected between neutral and ground so that the fault current does not exceed 3.75 pu if a single line to ground fault occurs at the terminals is _______ (assume fault impedance to be zero).Correct answer is between '0.1,0.1'. Can you explain this answer? tests, examples and also practice GATE tests.
    Explore Courses for GATE exam
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev