In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of air
  • a)
    7°C
  • b)
    12°C
  • c)
    9.5°C
  • d)
    14°C
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
In a certain cooling dehumidification operation, 360 kg/h of air (DBT ...
View all questions of this test
Most Upvoted Answer
In a certain cooling dehumidification operation, 360 kg/h of air (DBT ...
Free Test
Community Answer
In a certain cooling dehumidification operation, 360 kg/h of air (DBT ...
Understanding the Problem
To determine the outlet conditions of air after passing over a cooling coil, we need to analyze the cooling and dehumidification process using the given parameters:
- Air Flow Rate: 360 kg/h
- Dry Bulb Temperature (DBT): 35°C
- Relative Humidity (RH): 50%
- Apparatus Dew Point (ADP): 5°C
- Bypass Factor (BF): 15%
Key Concepts
- Apparatus Dew Point (ADP): This is the temperature at which air begins to condense moisture when cooled.
- Bypass Factor (BF): This indicates the fraction of air that does not come in contact with the cooling coil and thus does not get cooled to the ADP.
Calculating Outlet Conditions
1. Effective Cooling Temperature:
- The effective cooling temperature can be calculated using the formula:
- Effective Temperature = ADP + (BF x (DBT - ADP))
- Plugging in the values:
- Effective Temperature = 5 + (0.15 x (35 - 5))
- Effective Temperature = 5 + (0.15 x 30) = 5 + 4.5 = 9.5°C
2. Final Outlet Conditions:
- The calculated effective temperature of 9.5°C indicates the final outlet condition of the air after passing over the cooling coil.
Conclusion
The outlet conditions of the air after going over the cooling coil with a bypass factor of 15% results in an effective cooling temperature of 9.5°C, confirming that option 'C' is correct.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Question Description
In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? for Mechanical Engineering 2025 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer?.
Solutions for In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer?, a detailed solution for In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? has been provided alongside types of In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In a certain cooling dehumidification operation, 360 kg/h of air (DBT 35°C & RH 50%) is blown over a cooling coil having apparatus dew point of 5°C, assuming a bypass factor 15% determine outlet conditions of aira)7°Cb)12°Cc) 9.5°Cd)14°CCorrect answer is option 'C'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev