The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.?
Most Upvoted Answer
The 11-kV busbars of a power station are in two sections inter-connect...
Problem Statement

The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.

Solution

Step 1: Find the maximum short circuit current

The maximum short circuit current is given by the formula:

$I_{SC}=2\times\frac{MVA}{\sqrt{3}\times V_{L-L}\times Z\%}$

where,
MVA = 25 (rated MVA of each generator)
V_{L-L} = 11 kV (line to line voltage)
Z\% = 18% (sub-transient reactance)

Substituting these values, we get:

$I_{SC}=2\times\frac{25}{\sqrt{3}\times 11\times Z\%}$
$I_{SC}=2\times\frac{25}{\sqrt{3}\times 11\times 0.18}$
$I_{SC}=2549.17\text{ A}$

Step 2: Find the fault current

Since it is a symmetrical 3-phase fault, the fault current is given by:

$I_{f}=\frac{\sqrt{3}\times V_{L-L}}{Z_{eq}}$

where,
Z_{eq} = Z + X (reactance of the limiting reactor X)

Substituting the given values, we get:

$I_{f}=\frac{\sqrt{3}\times 11}{Z+X}$

Step 3: Find the maximum value of X

To prevent the circuit breaker from being overloaded, the fault current must not exceed the rated current of the circuit breaker. Therefore, we have:

$I_{f}\leq\frac{500}{\sqrt{3}\times 11}$

Substituting the values and solving for X, we get:

$X\geq Z\times\left(\frac{\sqrt{3}\times 11}{500}-1\right)$

$X\geq 0.22Z\%$

$X\geq 0.22\times 0.18$

$X\geq 0.0396$

Therefore, the reactance of the reactor X must be greater than or equal to 0.0396 pu to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.

Explanation

The given problem requires us to find the reactance of the current limiting reactor X to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders. To solve this problem, we first need to calculate the maximum short circuit current that can occur in the system. This is done using the formula for short circuit current. Once we know the maximum short circuit current, we can calculate the fault current that
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.?
Question Description
The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.?.
Solutions for The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? defined & explained in the simplest way possible. Besides giving the explanation of The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.?, a detailed solution for The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? has been provided alongside types of The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? theory, EduRev gives you an ample number of questions to practice The 11-kV busbars of a power station are in two sections inter-connected through a current limiting reactor X. Each section of the busbars is fed from two 11 kV, 25 MVA generators each having sub-transient reactance of 18% on its rating. The MVA rating of the circuit breaker is 500. Find the reactance of the reactor to prevent the circuit breaker from being overloaded if a symmetrical 3-phase fault occurs at one of the outgoing feeders.? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev