Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as following
Generator G1 : 11 kV, 40 MVA, 15%
Generator G2 : 11 kV, 20 MVA, 10%
Generator G3 : 11 kV, 20 MVA, 10%
Transformer T1 : 40 MVA, 11/66 kV, 15%
Transformer T2 : 40 MVA, 66/11 kV, 15%
Transformer T3: 5 MVA, 11/66 kV, 8%
If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)
Correct answer is '2.6'. Can you explain this answer?
Verified Answer
Two generating stations are connected together through transformers a...
Let base MVA is 40 MVA and base voltage is 11 kV, reactances on this base will be
Note : Generally the highest MVA should be selected as base for simplicity.
Equivalent circuit diagram is shown below
Applying KCL at node V,
View all questions of this test
Most Upvoted Answer
Two generating stations are connected together through transformers a...
Let base MVA is 40 MVA and base voltage is 11 kV, reactances on this base will be
Note : Generally the highest MVA should be selected as base for simplicity.
Equivalent circuit diagram is shown below
Applying KCL at node V,
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Question Description
Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? for Electrical Engineering (EE) 2025 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer?.
Solutions for Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer?, a detailed solution for Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? has been provided alongside types of Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two generating stations are connected together through transformers and a transmission line as shown in figure. The component specification are given as followingGenerator G1 : 11 kV, 40 MVA, 15%Generator G2 : 11 kV, 20 MVA, 10%Generator G3 : 11 kV, 20 MVA, 10%Transformer T1 : 40 MVA, 11/66 kV, 15%Transformer T2 : 40 MVA, 66/11 kV, 15%Transformer T3: 5 MVA, 11/66 kV, 8%If a three phase fault occurs as shown in figure, the fault current in kA at LV side of is _____. (Correct upto two decimal place)Correct answer is '2.6'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam
Signup to solve all Doubts
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev