In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.
The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.
    Correct answer is '17.1'. Can you explain this answer?
    Most Upvoted Answer
    In the power system (at no load) shown each generator has positive an...
    Given: Generators G1, G2, G3:
    Positive sequence network,
    Similarly, negative sequence network,
    Zero sequence Network,
    For LG Fault, sequence diagram is given by,
    Hence, the fault current feed to ground for LG fault at F is 17.1 pu.
    Free Test
    Community Answer
    In the power system (at no load) shown each generator has positive an...
    Given: Generators G1, G2, G3:
    Positive sequence network,
    Similarly, negative sequence network,
    Zero sequence Network,
    For LG Fault, sequence diagram is given by,
    Hence, the fault current feed to ground for LG fault at F is 17.1 pu.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer?
    Question Description
    In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer?.
    Solutions for In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer?, a detailed solution for In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? has been provided alongside types of In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In the power system (at no load) shown each generator has positive and negative sequence reactance of 10% and zero sequence reactance of 4%. The transmission line is having reactance of 8%. The generators are star connected with neutral solidly grounded. Assume that zero sequence reactance of line is 250% of its positive sequence.The magnitude of pu fault current feed to ground for LG fault at F is ____________ pu.Correct answer is '17.1'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev