) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load?
Most Upvoted Answer
) A 100 MVA generator with 10% reactance and a 200 MVA generator with ...

b Calculations for Bus 1:
- Given that the fault level on bus 1 is limited to 1500 MVA
- Let the reactance of the bus bar reactor X be Xpu on a 100 MVA base
- Xpu = X/(100^2) = X/10000

b Calculation for X:
- The fault level at bus 1 is limited to 1500 MVA
- Xpu = (1500 - 100)/(100^2) = 14/10000
- X = 10000 * 0.0014 = 14 Ω

b Calculations for Bus 2:
- Fault MVA at bus 2 can be calculated using the reactance of the 200 MVA generator
- Xpu = 8/(200^2) = 8/40000 = 0.0002
- Fault MVA at bus 2 = Xpu * 100^2 = 0.0002 * 10000 = 2 MVA

b Calculation for Circuit Breaker C:
- The fault MVA at bus 2 is 2 MVA
- The feeder has a reactance of 15%
- Total fault MVA at bus 2 = 2/(1-0.15) = 2/0.85 = 2.35 MVA
- MVA rating of circuit breaker C should be greater than 2.35 MVA

b Conclusion:
- The value of the reactance of the bus bar reactor X is 14 Ω
- The fault MVA at bus 2 is 2 MVA
- The MVA rating of circuit breaker C should be greater than 2.35 MVA to handle the fault level at bus 2.
Attention Mechanical Engineering Students!
To make sure you are not studying endlessly, EduRev has designed Mechanical Engineering study material, with Structured Courses, Videos, & Test Series. Plus get personalized analysis, doubt solving and improvement plans to achieve a great score in Mechanical Engineering.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load?
Question Description
) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load?.
Solutions for ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? defined & explained in the simplest way possible. Besides giving the explanation of ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load?, a detailed solution for ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? has been provided alongside types of ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? theory, EduRev gives you an ample number of questions to practice ) A 100 MVA generator with 10% reactance and a 200 MVA generator with 8% reactance are connected as shown in figure. Choose the base MVA as 100 MVA. i. If the fault level on bus 1 is limited to be 1500 MVA, calculate value of the reactance of bus bar reactor X. ii. Calculate fault MVA at bus 2. iii. Calculate MVA rating of circuit breaker C. 100 MVA 200 MVA 10% 8% Bus 1 Bus 2 Feeder 15% ON 100 MVA BASE Load? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev