In differential protection of busbars, the CT ratio is

  • a)
    Based on total expected fault current

  • b)
    Equal and based on primary current of lowest current carrying feeder

  • c)
    Based on their respective feeder current

  • d)
    is based on primary current input to secondary current output at full load.

Correct answer is option 'D'. Can you explain this answer?
Verified Answer
In differential protection of busbars, the CT ratio isa)Based on total...
In early days only conventional over current relays were used for busbar protection. But it is desired that fault in any feeder or transformer connected to the busbar should not disturb busbar system. In viewing of this time setting of busbar protection relays are made lengthy. So when faults occurs on busbar itself, it takes much time to isolate the bus from source which may came much damage in the bus system.
In recent days, the second zone distance protection relays on incoming feeder, with operating time of 0.3 to 0.5 seconds have been applied for busbar protection.
But this scheme has also a main disadvantage. This scheme of protection can not discriminate the faulty section of the busbar.
Now days, electrical power system deals with huge amount of power. Hence any interruption in total bus system causes big loss to the company. So it becomes essential to isolate only faulty section of busbar during bus fault.
View all questions of this test
Most Upvoted Answer
In differential protection of busbars, the CT ratio isa)Based on total...
Introduction:
Differential protection is a commonly used method for protecting busbars in electrical power systems. It involves the use of current transformers (CTs) to measure the current flowing through the busbars and detect any fault conditions. The CT ratio plays a crucial role in the proper functioning of differential protection.

Explanation:

CT Ratio:
The CT ratio refers to the ratio between the primary current input to the secondary current output of the CT. It determines the transformation ratio of the CT and is an essential parameter for accurate current measurement.

Primary Current:
The primary current refers to the current flowing through the busbars or feeders that are being protected by the differential protection scheme. Each feeder has its own primary current, which may vary depending on the load and configuration of the system.

Secondary Current:
The secondary current refers to the current output of the CT, which is proportional to the primary current. It is the current that is measured and used for differential protection.

Explanation of Options:
a) Based on total expected fault current:
This option suggests that the CT ratio is determined based on the total expected fault current. However, this is not correct as the CT ratio is not directly related to the fault current.

b) Equal and based on primary current of lowest current carrying feeder:
This option suggests that all the CT ratios are equal and based on the primary current of the feeder with the lowest current. This is not accurate as CT ratios should be determined based on the actual primary current of each feeder, not just the lowest one.

c) Based on their respective feeder current:
This option suggests that the CT ratio for each feeder is based on its respective current. This is partially correct, as the CT ratio should indeed be determined based on the primary current of each feeder.

d) Based on primary current input to secondary current output at full load:
This option is the correct answer. The CT ratio should be determined based on the primary current input to the secondary current output at full load. This means that the CT should be able to accurately measure the primary current and provide a proportional secondary current output under normal operating conditions.

Conclusion:
In conclusion, the CT ratio in the differential protection of busbars is based on the primary current input to the secondary current output at full load. This ensures accurate measurement of the primary current and proper functioning of the differential protection scheme.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Question Description
In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2025 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer?.
Solutions for In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer?, a detailed solution for In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? has been provided alongside types of In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In differential protection of busbars, the CT ratio isa)Based on total expected fault currentb)Equal and based on primary current of lowest current carrying feederc)Based on their respective feeder currentd)is based on primary current input to secondary current output at full load.Correct answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev