A 150 MVA, 22 kV synchronous generator having a reactance of = 0.2 pu,xd = 1.1pu is connected to a transformer through a 5-cycle circuit breaker.
The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -
    Correct answer is between '17.5,17.7'. Can you explain this answer?
    Verified Answer
    A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,x...
    Momentary current = 
    Sustained short circuit current = 
    The ratio of momentary current to sustained short circuit current of breaker = 
    View all questions of this test
    Most Upvoted Answer
    A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,x...
    Momentary current = 
    Sustained short circuit current = 
    The ratio of momentary current to sustained short circuit current of breaker = 
    Free Test
    Community Answer
    A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,x...
    Momentary current = 
    Sustained short circuit current = 
    The ratio of momentary current to sustained short circuit current of breaker = 
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer?
    Question Description
    A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer?.
    Solutions for A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer?, a detailed solution for A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? has been provided alongside types of A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 150 MVA, 22 kV synchronous generator having a reactance of= 0.2 pu,xd = 1.1puis connected to a transformer through a 5-cycle circuit breaker.The generator is at no load and rated voltage when a three-phase short circuit fault occurs between the breaker and transformer. The ratio of momentary current to sustained short circuit current of breaker is -Correct answer is between '17.5,17.7'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev