Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.
    Correct answer is between '0.9,0.91'. Can you explain this answer?
    Verified Answer
    Two wattmeter’s are connected to measure the power consumed by a...
    P1 = 1400 W, P2 = 800 W

    = 25.28°
    Power factor, cos ϕ = cos 25.28° = 0.90
    View all questions of this test
    Most Upvoted Answer
    Two wattmeter’s are connected to measure the power consumed by a...
    Given Information:
    - Two wattmeter readings: 1400 W and 800 W
    - Balanced 3-phase load

    Calculating Total Power:
    - Total power consumed by the load can be calculated by adding the readings of both wattmeters.
    - Total power = 1400 W + 800 W = 2200 W

    Calculating Power Factor:
    - Power factor (PF) can be calculated using the formula: PF = (P1 - P2) / (P1 + P2)
    - Substituting the values: PF = (1400 - 800) / (1400 + 800) = 600 / 2200 ≈ 0.2727

    Calculating Power Factor Angle:
    - The power factor angle (θ) can be calculated using the formula: θ = cos^(-1)(PF)
    - Substituting the power factor value: θ ≈ cos^(-1)(0.2727) ≈ 73.36 degrees

    Interpreting the Result:
    - Since both wattmeter readings are positive, the power factor angle should be in the first quadrant.
    - Power factor angle in the first quadrant ranges from 0 to 90 degrees.
    - Therefore, the power factor is between 0.9 to 0.91, as the calculated angle of 73.36 degrees falls in this range.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer?
    Question Description
    Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer?.
    Solutions for Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer?, a detailed solution for Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? has been provided alongside types of Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two wattmeter’s are connected to measure the power consumed by a 3-phase balanced load one of the wattmeter’s reads 1400 W and the other is 800 W. The power factor of the load is when both the readings are positive.Correct answer is between '0.9,0.91'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev