A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?
  • a)
    -7.13 MVAR
  • b)
    -13.33 MVAR
  • c)
    -6.2 MVAR
  • d)
    -19.53 MVAR
Correct answer is option 'A'. Can you explain this answer?
Verified Answer
A single – phase inductive load is drawing 10 MW at 0.6 power fa...
Initially when the real power is 10 MW and power factor is 0.6, the reactive power is 
Now when the capacitor is added, improved power factor is
cos-1 0.85 = 31.79°
Reactive power is 10 tan 31.79° = 6.2 VAR

Reactive power needed for the capacitor
= Qc = - (13.33 – 6.2)
= - 7.13 MVAR
View all questions of this test
Most Upvoted Answer
A single – phase inductive load is drawing 10 MW at 0.6 power fa...
A single what? Please provide more context or information so that I can better understand and provide a proper response.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer?
Question Description
A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer?.
Solutions for A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A single – phase inductive load is drawing 10 MW at 0.6 power factor lagging. A capacitor is added in parallel across the load to improve the power factor to 0.85. What is the reactive power required for the capacitor?a)-7.13 MVARb)-13.33 MVARc)-6.2 MVARd)-19.53 MVARCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev