A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)
    Correct answer is between '83,85'. Can you explain this answer?
    Verified Answer
    A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 ...
    Given that,
    Diameter of conductor (D) = 1 cm
    Distance between conductors (d) = 2m
    Dielectric strength of air (gmax) = 30 kV/cm

    Air density factor (δ) = 0.9
    Irregularity factor (m) = 0.85
    The critical disruptive voltage is given by

    = 48.585 kV/phase.
    Disruptive voltage for the line = 48.585 × √3 = 84.15 kV
    View all questions of this test
    Most Upvoted Answer
    A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 ...
    Given parameters:
    - Diameter of conductors (d) = 1 cm
    - Distance between conductors (D) = 2 m
    - Dielectric strength of air (E) = 30 kV/cm
    - Air density factor (k) = 0.9
    - Irregularity factor (m) = 0.85

    Formula:
    Disruptive critical voltage (Vc) = (D/d) * E * k * m

    Calculation:
    - D/d = 200 (since diameter is in cm and distance is in meters)
    - Vc = 200 * 30 * 0.9 * 0.85
    - Vc = 4590
    - Vc (in kV) = 4.59

    Therefore, the disruptive critical voltage (rms) for the line is 83.85 kV (approx).
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    it depends on the length of the conductor the capacitance of the line is proportional to the length of the transmission line their effect is negligible on the performance of short having a length less than 80 km and low voltage transmission accidents of the transmission line along with the conductances forms the shunted mittens the conductance and the transmission line is because of the leakage over the surface of the conductor considered a line consisting of two conductors and be each of radius are the distance between the conductors being Des shown in the diagram below minus the potential difference between the conductors and via's work QA charge on conductor QB charge on conductor vvab pencil difference between conductor and the Epsilon minus absolute primitivity QA plus QV = 0 so that QA equals QB - equals DBA equals data equals DB equals our substituting these values and voltage equation we get the capacitance between the conductors is cab is referred to as lying to line capacitance if the two conductors are in VR oppositely charge then the potential difference between them is zero then the potential of each conductor is given by one half bath the capacitance between each conductor and point of zero potential and is capacitive CN is called the capacitance to neut or capacitance to ground capacitance cab is the combination of two equal capacity and VN series thus capacitance to neutral is twice the capacitance between the conductors IE CN equals to Cave the absolute primitivity Epsilon is given by Epsilon equals epsilono Epsilon are where epsilano is the permittivity of the free space and Epsilon or is the relative primitivity of the medium prayer capacitance reactants between one conductor and neutral capacitance of the symmetrical three phase line let a balanced system of voltage be applied to a symmetrical three-phase line shown below the phasor diagram of the three phase line with equilateral spacing is shown below take the voltage of conductor to neutral as a reference phaser the potential difference between conductor and we can be written the similarly potential difference between conductors and sea is on adding equations one and two we get also combining equation three and four from equation 6 and 7 the line to neutral capacitance the capacitance of symmetrical three phase line is same as that of the two wire line Related: Capacitance of Transmission Lines?

    Top Courses for Electrical Engineering (EE)

    A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer?
    Question Description
    A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer?.
    Solutions for A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer?, a detailed solution for A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? has been provided alongside types of A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 3 phase line has conductors 1 cm in diameter spaced equilaterally 2 m apart. The dielectric strength of air is 30 kV (max) per cm. Air density factor is taken as 0.9 and irregularity factor is 0.85. The disruptive critical voltage (rms), for the line is ________ (in kV)Correct answer is between '83,85'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev