Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.
  • a)
    56.47 HZ
  • b)
    57.90 HZ
  • c)
    59.23 HZ
  • d)
    51.56 HZ
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
Two generators rated 250 MW and 400 MW are operating in parallel. The ...
Let, Load on generator 1 = x MW
Load on generator 2 = (450 – x) MW
Reduction in frequency = Δf
Now,

 
∴ x = 217.81 MW (load on generator 1)
450 – x = 232.18 MW (load on generator 2)
and Δf = 2.09Hz
∴ System frequency = (60 – 2.09) = 57.909 Hz.
View all questions of this test
Most Upvoted Answer
Two generators rated 250 MW and 400 MW are operating in parallel. The ...
Given:
Two generators rated 250 MW and 400 MW are operating in parallel.
Droop characteristics of the governors are 4% and 6% respectively.
Load shared between them is 450 MW.
Nominal system frequency is 60 Hz.
No governing action.

To find:
System frequency

Solution:
1. Calculate the total capacity of the generators:
Total capacity = 250 MW + 400 MW = 650 MW

2. Calculate the droop constant for each generator:
Droop constant = 100 / droop percentage

Droop constant for generator 1 = 100 / 4 = 25
Droop constant for generator 2 = 100 / 6 = 16.67

3. Calculate the load shared by each generator:
Load shared by generator 1 = (Generator 1 capacity / Total capacity) * Total load
= (250 MW / 650 MW) * 450 MW
= 173.08 MW

Load shared by generator 2 = (Generator 2 capacity / Total capacity) * Total load
= (400 MW / 650 MW) * 450 MW
= 276.92 MW

4. Calculate the frequency deviation for each generator:
Frequency deviation = (Load shared by generator / Generator capacity) * Droop constant

Frequency deviation for generator 1 = (173.08 MW / 250 MW) * 25
= 17.92

Frequency deviation for generator 2 = (276.92 MW / 400 MW) * 16.67
= 11.54

5. Calculate the overall frequency deviation:
Overall frequency deviation = Frequency deviation for generator 1 + Frequency deviation for generator 2

= 17.92 + 11.54
= 29.46

6. Calculate the change in frequency:
Change in frequency = (Overall frequency deviation / Total capacity) * 100

= (29.46 / 650 MW) * 100
= 4.53 Hz

7. Calculate the system frequency:
System frequency = Nominal system frequency - Change in frequency

= 60 Hz - 4.53 Hz
= 55.47 Hz

Therefore, the system frequency will be 55.47 Hz, which is closest to option B (57.90 Hz).
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer?
Question Description
Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer?.
Solutions for Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer?, a detailed solution for Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? has been provided alongside types of Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two generators rated 250 MW and 400 MW are operating in parallel. The droop characteristics of the governors are 4% and 6% respectively.if a load of 450 MW is share between them. What will be the system frequency? Assume nominal system frequency is 60 Hz and no governing action.a)56.47 HZb)57.90 HZc)59.23 HZd)51.56 HZCorrect answer is option 'B'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev