Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the  load shared by the larger  unit is _______ MW.
    Correct answer is between '395,405'. Can you explain this answer?
    Verified Answer
    Two generating units rated 300 MW and 400 MW have governor speed regul...
    Assume No – load speed regulations are equal 
    From similar triangles method
    Given that P1 + P2 = 600MW
    150x = 600
    x = 4
    ∴The load supplied by largest machine is P2 = 100 x 4 = 400MW
    View all questions of this test
    Most Upvoted Answer
    Two generating units rated 300 MW and 400 MW have governor speed regul...
    Given data:
    - Two generating units rated 300 MW and 400 MW
    - Governor speed regulation of 6% and 4% respectively
    - Operating in parallel to share a load of 600 MW

    To find:
    - Load shared by the larger unit

    Solution:
    1. Determine the speed regulation constant (K) for each generator:
    - K = 100 / (% speed regulation)
    - For 300 MW unit: K = 100 / 6 = 16.67
    - For 400 MW unit: K = 100 / 4 = 25

    2. Determine the droop (Ds) for each generator:
    - Ds = (K / 100) * (rated power / total load)
    - For 300 MW unit: Ds = (16.67 / 100) * (300 / 600) = 0.0833
    - For 400 MW unit: Ds = (25 / 100) * (400 / 600) = 0.1667

    3. Calculate the actual load shared by each generator:
    - For 300 MW unit: actual load = 300 + (0.0833 * (600 - 300)) = 341.65 MW
    - For 400 MW unit: actual load = 400 + (0.1667 * (600 - 400)) = 405.01 MW

    4. Therefore, the load shared by the larger unit (400 MW) is approximately 405 MW.

    Answer: 405 MW
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer?
    Question Description
    Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer?.
    Solutions for Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer?, a detailed solution for Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? has been provided alongside types of Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two generating units rated 300 MW and 400 MW have governor speed regulation of 6% and 4% respectively from no load to full load. Both the generating units are operating in parallel to share a load of 600 MW. Assuming free governor action, the load shared by the larger unit is _______ MW.Correct answer is between '395,405'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev