Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).
    Correct answer is '200'. Can you explain this answer?
    Most Upvoted Answer
    Two generating units rated for 250 MW and 400 MW have governor speed r...
    Given:
    Two generating units rated for 250 MW and 400 MW respectively.
    Governor speed regulations of the units are 6% and 6.4% from no load to full load.
    Both units are operating in parallel to share a load of 500 MW.

    To find the load shared by the 250 MW generating unit, we can use the concept of droop characteristics.

    Droop Characteristics:
    The droop characteristic of a generator determines how much the speed of the generator will decrease as the load increases. It is expressed as a percentage change in speed from no-load to full-load conditions.

    The formula to calculate the load shared by a generator in a parallel operation is:
    Load shared = (Generator rating / Total rating) * Total load

    Calculations:
    1. Calculate the total rating of the generating units:
    Total rating = 250 MW + 400 MW = 650 MW

    2. Calculate the droop for each generating unit:
    Droop for 250 MW unit = 6%
    Droop for 400 MW unit = 6.4%

    3. Calculate the load shared by the 250 MW generating unit:
    Load shared = (250 MW / 650 MW) * 500 MW
    Load shared = (0.3846) * 500 MW
    Load shared ≈ 192.3 MW

    4. Round off the load shared to the nearest integer:
    Load shared ≈ 192 MW (rounded off to the nearest integer)

    Therefore, the load shared by the 250 MW generating unit is approximately 192 MW, which rounds off to 200 MW as the nearest integer.

    Summary:
    The load shared by the 250 MW generating unit in parallel operation with a 400 MW unit, both with governor speed regulations of 6% and 6.4% respectively, is approximately 200 MW.
    Free Test
    Community Answer
    Two generating units rated for 250 MW and 400 MW have governor speed r...
    Equation (i) divide by equation (ii),
    Pa = 200 MW
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer?
    Question Description
    Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer?.
    Solutions for Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer?, a detailed solution for Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? has been provided alongside types of Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two generating units rated for 250 MW and 400 MW have governor speed regulations of 6% and 6.4%, respectively, from no load to full load. Both the generating units are operating in parallel to share a load of 500 MW. Assuming free governor action, the load shared in MW, by the 250 MW generating unit is ____ . (round off to nearest integer).Correct answer is '200'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev