The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.
    Correct answer is between '2.2,2.3'. Can you explain this answer?
    Verified Answer
    The ratio of starting to full load current for a 15 kW, 300 V and 3 ...
    Ist = 30 A
    Starting current when it work at 300V
    Ist = 30 × 3 = 90 A

    ∴ Ratio of starting current to full load current
    = 90/40.09 = 2.244
    View all questions of this test
    Most Upvoted Answer
    The ratio of starting to full load current for a 15 kW, 300 V and 3 ...
    Given data:
    - Power rating of the motor (P) = 15 kW
    - Voltage rating of the motor (V) = 300 V
    - Number of phases (N) = 3
    - Full load efficiency (η) = 0.90
    - Power factor (PF) = 0.8
    - Short-circuit current (Isc) = 30 A
    - Short-circuit voltage (Vsc) = 100 V

    1. Finding the full load current (Ifl):
    The full load current (Ifl) can be calculated using the formula:
    Ifl = P / (V * √3)
    Substituting the given values:
    Ifl = 15,000 W / (300 V * √3)
    Ifl ≈ 27.39 A

    2. Finding the starting current (Istart):
    The starting current (Istart) for a direct-on-line (DOL) starter is typically 6 to 7 times the full load current (Ifl). Therefore, we can assume Istart = 6 * Ifl.
    Istart ≈ 6 * 27.39 A
    Istart ≈ 164.34 A

    3. Finding the ratio of starting to full load current:
    The ratio of starting to full load current is given by:
    Ratio = Istart / Ifl
    Substituting the values:
    Ratio ≈ 164.34 A / 27.39 A
    Ratio ≈ 5.997

    4. Analyzing the correct answer:
    The correct answer is stated to be between 2.2 and 2.3. However, the calculated ratio is approximately 5.997, which is not within the given range. Therefore, the given answer is incorrect.

    Conclusion:
    The ratio of starting to full load current for the 15 kW, 300 V, 3-phase induction motor with a DOL starter is approximately 5.997. The correct answer is not between 2.2 and 2.3, as stated.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer?
    Question Description
    The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer?.
    Solutions for The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer?, a detailed solution for The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? has been provided alongside types of The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The ratio of starting to full load current for a 15 kW, 300 V and 3ϕ induction motor with DOL starter is _________. For 3 phase inductor motor has full load efficiency 0.90 the full load PF is 0.8 and short-circuit current is 30A at 100V.Correct answer is between '2.2,2.3'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev