A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?
  • a)
    78.6 + j 608.2
  • b)
    72.6 + j 508.2
  • c)
    62.6 + j 908.2
  • d)
    65.6 + j 786.2
Correct answer is option 'B'. Can you explain this answer?
Verified Answer
A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resista...
∴ Its base impedance

The PU impedance of the transformer is
Zeq = [0.01 + j 0.07] PU
So the high-side impedance in ohm is
Zeq = Zeq pu × Zbase
= (0.01 + j0.07) × 7260 Ω
= 72.6 + j 508.2
View all questions of this test
Most Upvoted Answer
A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resista...
Transformer is a type of electrical transformer that has a maximum output of 50 kilovolt-amperes (kVA) and a primary voltage rating of 11,000 volts (V) and a secondary voltage rating of 400 volts (V). This type of transformer is commonly used to step down high voltage power supply from transmission lines to lower voltage levels suitable for distribution in commercial and residential areas. It is also used in industrial applications for powering machinery and equipment. The transformer is designed to convert electrical energy from one voltage level to another, while maintaining the frequency and power of the input signal.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer?
Question Description
A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer?.
Solutions for A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer?, a detailed solution for A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? has been provided alongside types of A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 50 KVA, 11000/400 V Δ-Y distribution transformer has a resistance of 1% and reactance of 7% per unit. What is the transformer phase impedance referred to the high-voltage side?a)78.6 + j 608.2b)72.6 + j 508.2c)62.6 + j 908.2d)65.6 + j 786.2Correct answer is option 'B'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev