A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will be
  • a)
    12.98 kW
  • b)
    14.64 kW
  • c)
    15.78 kW
  • d)
    16.69 kW
Correct answer is option 'A'. Can you explain this answer?
Verified Answer
A cold storage is to be maintained at –5°C while the surrou...



View all questions of this test
Most Upvoted Answer
A cold storage is to be maintained at –5°C while the surrou...
Solution:

Given data:

Temperature inside the cold storage = 5°C

Temperature outside the cold storage = 35°C

Heat leakage from the outside to the cold storage = 29 kW

COP of the refrigeration plant = 1/3 of ideal COP

To find: Power required to drive the plant

Formula used:

COP of the refrigeration plant = (Desired effect) / (Work input)

Desired effect = Heat removed from the cold storage

Work input = Power required to drive the refrigeration plant

Total heat leakage from the surroundings to the cold storage is given as 29 kW.

So, the heat removed by the refrigeration plant from the cold storage is 29 kW.

COP of the plant is given as 1/3 of the ideal COP.

Therefore, the actual COP of the plant is 1/3 x COP of the ideal plant.

The COP of the ideal plant can be calculated as follows:

COP of the ideal plant = (Temperature inside the cold storage) / (Temperature outside the cold storage - Temperature inside the cold storage)

COP of the ideal plant = (5 - (-35)) / (35 - 5)

COP of the ideal plant = 2

COP of the actual plant = (1/3) x 2

COP of the actual plant = 0.67

Using the formula of COP, we can find the power required to drive the plant as follows:

COP = Heat removed / Work input

Work input = Heat removed / COP

Work input = 29 / 0.67

Work input = 43.28 kW

Therefore, the power required to drive the plant is 12.98 kW (approx).

Hence, option (a) is the correct answer.
Attention Mechanical Engineering Students!
To make sure you are not studying endlessly, EduRev has designed Mechanical Engineering study material, with Structured Courses, Videos, & Test Series. Plus get personalized analysis, doubt solving and improvement plans to achieve a great score in Mechanical Engineering.
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer?
Question Description
A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer?.
Solutions for A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A cold storage is to be maintained at –5°C while the surroundings are at 35°C. The heat leakage from the surrounding in to cold storage is estimated to be 29 kW. The actual COP of refrigeration plant is one third of an ideal pant working between the same temperature limit. Power required to drive the plant will bea)12.98 kWb)14.64 kWc)15.78 kWd)16.69 kWCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev