A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will be
  • a)
    196.44 Ω
  • b)
    286.62 Ω
  • c)
    250 Ω
  • d)
    290.43 Ω
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The li...
Surge impedance of the line is given by

or, 
View all questions of this test
Most Upvoted Answer
A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The li...
ΜF/km per phase. The resistance is negligible. Assuming the voltage at the sending end of the line is 400 kV, determine:

a) The receiving end voltage when the line is delivering 800 MW.

b) The maximum power that can be transmitted through the line without exceeding a voltage drop of 10% of the sending end voltage.

c) The surge impedance of the line.

d) The capacitance reactance of the line per phase.

a) The receiving end voltage can be determined using the formula:

V_R = V_S - I_L Z_L - I_C Z_C

where V_S is the sending end voltage, I_L is the line current, Z_L is the line impedance, I_C is the capacitive current, and Z_C is the capacitive reactance.

First, we need to calculate the line impedance and capacitive reactance per phase:

Z_L = jωL = j2πfL = j2π50(0.97×10^-3)×300 = j138.6 Ω

Z_C = 1/jωC = -j1/(2πfC) = -j1/(2π50×0.0115×10^-6) = -j123.2 Ω

Next, we can calculate the line current:

I = P/(√3 V_S cos φ) = 800×10^6/(√3×400×10^3×1) = 1547.7 A

where cos φ = 1 (assuming unity power factor).

Finally, we can calculate the receiving end voltage:

V_R = 400×10^3 - j138.6×1547.7 - j123.2×1547.7 = 346.3∠-13.3° kV

Therefore, the receiving end voltage is 346.3 kV at an angle of -13.3° with respect to the sending end voltage.

b) The maximum power that can be transmitted through the line without exceeding a voltage drop of 10% of the sending end voltage can be determined using the formula:

P_max = 3 V_S^2/(2Z_L) (1 - V_R/V_S)

where V_R is the receiving end voltage and V_S is the sending end voltage.

We can rearrange this formula to solve for V_R:

V_R = V_S (1 - 2P_max Z_L/(3V_S^2))

Substituting the given values, we get:

V_R = 400×10^3 (1 - 2×P_max×138.6/(3×(400×10^3)^2))

When the voltage drop is 10% of the sending end voltage, V_R/V_S = 0.9. Solving for P_max, we get:

P_max = 3×(400×10^3)^2×(1 - 0.9)/(2×138.6×0.9) = 1600 MW

Therefore, the maximum power that can be transmitted through the line without exceeding a voltage drop of 10% of the sending end voltage is 1600 MW.

c) The surge impedance of the line can be calculated using the formula:

Z_0 = √(Z_L/Z_C) = √(j138.6/-j123.2)
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer?
Question Description
A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer?.
Solutions for A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A three-phase, 50 Hz, 400 kV, transmission line is 300 km long. The line inductance is 0.97 mH/km per phase and capacitance is 0.0115 μF/km per phase. Assuming a lossless line, the surge impedance of the line will bea)196.44Ωb)286.62Ωc)250Ωd)290.43ΩCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev