Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?
  • a)
    0.45
  • b)
    0.15
  • c)
    0.025
  • d)
    0.05
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
Three synchronous generators, each of which is rated to 100 MVA, 11 KV...
Using Thevenin's Theorem, Vth = V all the three impedances will be in parallel.
Single line diagram:
So, equivalent p.u. impedance of each generator is
Zth = Zn / 3 = 0.15 / 3 = 0.05 pu
Key Points
  • All generators are connected in parallel to increase current going to the line because all generators are at equal voltages.
  • Generators are shown with their impedances in a single line diagram.
Free Test
Community Answer
Three synchronous generators, each of which is rated to 100 MVA, 11 KV...
Calculation:

Given data:
- Number of generators: 3
- Rating of each generator: 100 MVA
- Voltage rating: 11 kV
- Impedance per unit: 0.15

To find:
- Effective per unit impedance of each generator when replaced by a single equivalent generator

Step 1: Calculation of equivalent impedance

The total impedance of the three generators connected in parallel can be calculated as follows:

Zeq = Zg / N

Where,
Zeq = Equivalent impedance
Zg = Impedance of a single generator
N = Number of generators

Given that Zg = 0.15, and N = 3, we can substitute these values into the equation:

Zeq = 0.15 / 3
Zeq = 0.05

Therefore, the equivalent impedance of the three generators connected in parallel is 0.05 per unit.

Step 2: Calculation of effective per unit impedance

To find the effective per unit impedance of each generator, we need to divide the equivalent impedance by the number of generators:

Effective per unit impedance = Zeq / N

Given that Zeq = 0.05 and N = 3, we can substitute these values into the equation:

Effective per unit impedance = 0.05 / 3
Effective per unit impedance = 0.0167

Therefore, the effective per unit impedance of each generator when replaced by a single equivalent generator is 0.0167.

Step 3: Comparing the options

a) 0.45 - This is not the correct answer.
b) 0.15 - This is not the correct answer.
c) 0.025 - This is not the correct answer.
d) 0.05 - This is the correct answer.

Therefore, option D, 0.05, is the correct answer.

Conclusion:

When three synchronous generators with an impedance per unit of 0.15 are replaced by a single equivalent generator, the effective per unit impedance of each generator becomes 0.05.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer?
Question Description
Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer?.
Solutions for Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer?, a detailed solution for Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? has been provided alongside types of Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Three synchronous generators, each of which is rated to 100 MVA, 11 KV, have an impedance per unit of 0.15. If all three generators are replaced by a single equivalent generator, what will be the effective per unit impedance of each generator?a)0.45b)0.15c)0.025d)0.05Correct answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev