Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A 30 MV A, 3-phase, 50Hz,13.8kV, star-connect... Start Learning for Free
A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases  ′b′and′c′, with a fault impedance of j0.1p.u. The value of  Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.
    Correct answer is between '1.05,1.15'. Can you explain this answer?
    Most Upvoted Answer
    A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator ...
    We have the base current 

    The positive sequence current, Ip = 4270 A

    Fault impedance = 0.1 pu
    Xn = 3zf + 0.05 + 3xn = 0.35 + 3xn 

    From above equation, we get  Xn = 1.07 p.u
    Free Test
    Community Answer
    A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator ...
    To calculate the fault current and the fault voltage in this scenario, we need to use the positive, negative, and zero sequence reactances of the generator.

    Let's assume the fault occurs between phases A and B. In a double line to ground fault, the fault current splits into three components: the positive sequence current (I1), the negative sequence current (I2), and the zero sequence current (I0).

    The fault current in each phase can be calculated using the following formula:

    I1 = (Vph / (√3 X1))
    I2 = (Vph / (√3 X2))
    I0 = (Vph / (√3 X0))

    Where:
    - Vph is the line-to-neutral voltage of the generator (13.8 kV / √3 = 7.98 kV)
    - X1, X2, and X0 are the positive, negative, and zero sequence reactances respectively (15%, 15%, and 5% of the generator's impedance, which is the sum of the positive and negative sequence reactances)

    Using these values, we can calculate the fault current:

    I1 = (7.98 kV / (√3 * 0.15)) = 30.97 kA
    I2 = (7.98 kV / (√3 * 0.15)) = 30.97 kA
    I0 = (7.98 kV / (√3 * 0.05)) = 92.91 kA

    The total fault current (If) is the vector sum of the positive, negative, and zero sequence currents:

    If = √(I1^2 + I2^2 + I0^2)
    = √((30.97 kA)^2 + (30.97 kA)^2 + (92.91 kA)^2)
    = 108.99 kA

    Next, let's calculate the fault voltage (Vf) across the faulted phases. The fault voltage can be calculated using the following formula:

    Vf = (Vph * (X1 + X2 + Xn)) / (√3 * (X1 + X2 + Xn + X0))

    Where:
    - Xn is the reactance connected between the neutral of the generator and ground

    Using the given values:

    Vf = (7.98 kV * (0.15 + 0.15 + Xn)) / (√3 * (0.15 + 0.15 + Xn + 0.05))

    Now, we need to know the value of Xn to calculate the fault voltage accurately. If you provide the value of Xn, we can calculate the fault voltage accordingly.
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer?
    Question Description
    A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer?.
    Solutions for A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer?, a detailed solution for A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? has been provided alongside types of A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 30 MV A, 3-phase, 50Hz,13.8kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%,15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phases ′b′and′c′, with a fault impedance of j0.1p.u. The value of Xn (in p.u.) that will limit the positive sequence generator current to 4270 A is _________.Correct answer is between '1.05,1.15'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev