Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A 3-phase grid-connected voltage source conve... Start Learning for Free
A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).
    Correct answer is '0.47'. Can you explain this answer?
    Most Upvoted Answer
    A 3-phase grid-connected voltage source converter with DC link voltage...
    Calculating Modulation Index for Sinusoidal PWM

    Given parameters:
    - DC link voltage (Vdc) = 1000 V
    - Grid phase current (Ig) = 10 A
    - Complex power supplied by the converter (S) = -4000 -j3000 VA

    To calculate the modulation index (m) for sinusoidal PWM, we need to use the following formula:

    m = (2/π) * sin^-1(sqrt(3/2) * (|S|/Vdc) / Ig)

    Here, |S| represents the magnitude of the complex power, and sqrt(3/2) is a constant factor for 3-phase systems.

    Substituting the given values in the formula, we get:

    m = (2/π) * sin^-1(sqrt(3/2) * (5000/1000) / 10)
    m = 0.47 (rounded off to two decimal places)

    Therefore, the modulation index used in sinusoidal PWM is 0.47.

    Explanation:

    Sinusoidal PWM is a technique used to control the output voltage of a voltage source converter (VSC) by modulating the width of the pulses in a sinusoidal waveform. The modulation index in sinusoidal PWM determines the amplitude of the output voltage waveform.

    In this question, we are given the DC link voltage, grid phase current, and complex power supplied by the converter. Using the formula for modulation index in sinusoidal PWM, we can calculate the value of the modulation index.

    The formula involves taking the inverse sine of a certain expression, which is a function of the complex power, DC link voltage, and grid phase current. By substituting the given values and simplifying the expression, we obtain the value of the modulation index as 0.47.

    This indicates that the amplitude of the output voltage waveform will be 47% of the DC link voltage.
    Free Test
    Community Answer
    A 3-phase grid-connected voltage source converter with DC link voltage...
    S = (-4000 - J3000) VA 
    VL1(rms) = 288.675 V
    3-φ VSI - SPWM,    MA ≤ 1
    MA = 0.47
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer?
    Question Description
    A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer?.
    Solutions for A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer?, a detailed solution for A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? has been provided alongside types of A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by (-4000 - j3000) VA, then the modulation index used in sinusoidal PWM is ____ . (round off to two decimal places).Correct answer is '0.47'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev