Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  Which of the following statement is incorrect... Start Learning for Free
Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?
  • a)
    Low-value resistance should be used with a galvanometer
  • b)
    Galvanometer should be properly shunted
  • c)
    Galvanometer should have high resistance
  • d)
    The cable should be immersed for 24 hours
Correct answer is option 'A'. Can you explain this answer?
Most Upvoted Answer
Which of the following statement is incorrect while taking precautions...
(a) The direct deflection method is used for the measurement of the insulation resistance of the cable. Following precautions should be taken while using the direct deflection method.
(b) Before testing the cable is immersed in water at least for 24 hours. The temperature of the water is maintained constant. The water enters through the pores if any, and soaks through the defects, and at the same time, the cable attains the temperature of the water.
(c) In the earlier phase of the measurement, the galvanometer must be properly shunted. It includes a series resistance of high value. The true value of insulation resistance can be determined by subtracting the value of series resistance from the observed resistance.
(d) While conducting tests on cables the galvanometer should be short-circuited before applying the voltage. The short-circuiting connection is removed only after sufficient time has elapsed so that charging and absorption currents cease to flow. 
(e) After the application of voltage, a short circuit connection across the galvanometer is removed. Thus galvanometer is protected from the sudden initial spike of current which charges cable which acts as a capacitor.
(f) The battery voltage should be around 500 V and should be maintained constant. The galvanometer should be highly sensitive (not less than 1000 mm per microampere at a scale distance of 1 metre), should have high resistance and also that its deflection should be directly proportional to the current flowing through it and should be critically damped.
(g) To prevent leakage currents, the galvanometer circuit switches and circuitry must be well insulated.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer?
Question Description
Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer?.
Solutions for Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Which of the following statement is incorrect while taking precautions for testing the cable using the direct deflection method?a)Low-value resistance should be used with a galvanometerb)Galvanometer should be properly shuntedc)Galvanometer should have high resistanced)The cable should be immersed for 24 hoursCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev