Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A 30 kV, 50 Hz, 50 MVA generator has the posi... Start Learning for Free
A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:
  • a)
    1 Ω
  • b)
    1.8 Ω
  • c)
    0.1 Ω
  • d)
    2.18 Ω
Correct answer is option 'B'. Can you explain this answer?
Most Upvoted Answer
A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero ...
Concept:
Fault current for LG fault =
Fault current for three phase fault =
where,
X= Positive sequence reactance
X2 = Negative sequence reactance
X= Zero sequence reactance
Xn = Grounding reactance
Calculation:
Given that,
X1 = 0.25 pu
X2 = 0.15 pu
X0 = 0.05 pu
Fault current for LG fault is 
Fault current for three phase fault,
Given that both the fault currents are equal.
⇒ Xn = 0.1 pu
Base kV = 30 kV
Base MVA = 50 MVA
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer?
Question Description
A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer?.
Solutions for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer?, a detailed solution for A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? has been provided alongside types of A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance is:a)1 Ωb)1.8 Ωc)0.1 Ωd)2.18 ΩCorrect answer is option 'B'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev