A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.
The sub transient current of the fault is ______ (in pu).
  • a)
    20
  • b)
    25
  • c)
    30
  • d)
    32
Correct answer is option 'A'. Can you explain this answer?
Most Upvoted Answer
A generator station having 4 identical generators which are connected ...
Given,
Z = 0.2 pu
4 parallel identical generators are connected to a common bus and a symmetrical fault occurred at the end of the line.
ER1 = 2.0pu

As ER1 not given assuming ER1 = 1pu
Xeq =Z/4, as 4 identical generators are connected to a common bus L-L-L fault is occurring at the line end as the fault is a symmetrical fault.
So, the fault current is:
Explore Courses for RRB NTPC/ASM/CA/TA exam

Top Courses for RRB NTPC/ASM/CA/TA

A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer?
Question Description
A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? for RRB NTPC/ASM/CA/TA 2024 is part of RRB NTPC/ASM/CA/TA preparation. The Question and answers have been prepared according to the RRB NTPC/ASM/CA/TA exam syllabus. Information about A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? covers all topics & solutions for RRB NTPC/ASM/CA/TA 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer?.
Solutions for A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for RRB NTPC/ASM/CA/TA. Download more important topics, notes, lectures and mock test series for RRB NTPC/ASM/CA/TA Exam by signing up for free.
Here you can find the meaning of A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer?, a detailed solution for A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? has been provided alongside types of A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A generator station having 4 identical generators which are connected to a common bus. The Impedance of each generator is 0.2 pu. A symmetrical fault takes place at the bus bar of the generator.The sub transient current of the fault is ______ (in pu).a)20b)25c)30d)32Correct answer is option 'A'. Can you explain this answer? tests, examples and also practice RRB NTPC/ASM/CA/TA tests.
Explore Courses for RRB NTPC/ASM/CA/TA exam

Top Courses for RRB NTPC/ASM/CA/TA

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev