In a certain cooling dehumidification operation 360 kg/h of air (DBT 350C & RH 50%) is blown over a cooling coil having apparatus dew point of 50C, assuming a bypass factor of 15%, the outlet temperature of air is
  • a)
    70C
  • b)
    120C
  • c)
    9.5
    0C
  • d)
    140c
Correct answer is option 'C'. Can you explain this answer?
Verified Answer
In a certain coolingdehumidification operation 360 kg/h of air (DBT 35...
View all questions of this test
Most Upvoted Answer
In a certain coolingdehumidification operation 360 kg/h of air (DBT 35...
Calculation:
- Given parameters:
- Inlet air conditions: DBT = 35°C, RH = 50%
- Apparatus dew point = 5°C
- Bypass factor = 15%

Step 1: Determine the coil outlet conditions
- Calculate the coil outlet conditions using the bypass factor formula:
- Tout = (1 - B) * Tdb + B * Tdp
- Tout = (1 - 0.15) * 35 + 0.15 * 5
- Tout = 0.85 * 35 + 0.15 * 5
- Tout = 29.75 + 0.75
- Tout = 30.5°C

Step 2: Check the options for the outlet temperature
- Compare the calculated outlet temperature (30.5°C) with the provided options:
- a) 70°C
- b) 120°C
- c) 9.5°C
- d) 14°C

Conclusion:
- The correct answer is option c) 9.5°C.
Attention Mechanical Engineering Students!
To make sure you are not studying endlessly, EduRev has designed Mechanical Engineering study material, with Structured Courses, Videos, & Test Series. Plus get personalized analysis, doubt solving and improvement plans to achieve a great score in Mechanical Engineering.
Explore Courses for Mechanical Engineering exam

Similar Mechanical Engineering Doubts

Top Courses for Mechanical Engineering

In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer?
Question Description
In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? for Mechanical Engineering 2024 is part of Mechanical Engineering preparation. The Question and answers have been prepared according to the Mechanical Engineering exam syllabus. Information about In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? covers all topics & solutions for Mechanical Engineering 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer?.
Solutions for In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? in English & in Hindi are available as part of our courses for Mechanical Engineering. Download more important topics, notes, lectures and mock test series for Mechanical Engineering Exam by signing up for free.
Here you can find the meaning of In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer?, a detailed solution for In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? has been provided alongside types of In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice In a certain coolingdehumidification operation 360 kg/h of air (DBT 350C & RH 50%) isblown over a cooling coil havingapparatus dew point of 50C,assuming a bypass factor of 15%,the outlet temperature of air isa)70Cb)120Cc)9.50Cd)140cCorrect answer is option 'C'. Can you explain this answer? tests, examples and also practice Mechanical Engineering tests.
Explore Courses for Mechanical Engineering exam

Top Courses for Mechanical Engineering

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev