Two power stations S1 and S2 are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1 has one generator of P.U. the reactance of 0.3, and station S2 has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2 removed, is _____ (in %).
    Correct answer is '20'. Can you explain this answer?
    Verified Answer
    Two power stations S1and S2are interconnected through a transmission l...
    Equivalent reactance with respect to fault point =(0.3 + 0.3) || (0.3 + (0.6 || 0.6))
    =0.6 || (0.3 + 0.3)
    = 0.3
    After removal of one of the generators of S2 with respect to fault point
    = (0.3 + 0.3) || (0.3 + 0.6)
    = (0.6) || (0.9) = 0.36
    Change in the reactance = 
    = 20%
    View all questions of this test
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer?
    Question Description
    Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer?.
    Solutions for Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer?, a detailed solution for Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? has been provided alongside types of Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice Two power stations S1and S2are interconnected through a transmission line of per unit (p.u) reactance of 0.6. Station S1has one generator of P.U. the reactance of 0.3, and station S2has two generators of p.u reactance 0.6 each. For a 3 – phase symmetrical short circuit at the middle of the transmission line (point F). The change in the value of the equivalent fault reactance, with one of the generators of S2removed, is _____ (in %).Correct answer is '20'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev