The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.

Find Induced voltage per phase (in volt) at the secondary side.
    Correct answer is between '263,265'. Can you explain this answer?
    Verified Answer
    The terminal voltage on the secondary side when supplying full load at...
    Percentage voltage Regulation
    = R cos ϕ + X sin ϕ
    = 1 × 0.8 + 5 × 0.6 = 3.8%
    We know that voltage regulation

    I.V. – 440 = 0.038 I.V
    I.V = 457.38
    View all questions of this test
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer?
    Question Description
    The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer?.
    Solutions for The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer?, a detailed solution for The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? has been provided alongside types of The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The terminal voltage on the secondary side when supplying full load at 0.8 lagging P.F. is 440 V. the equivalent Resistance and reactance drops for the transformer are 1% and 5% respectively.Find Induced voltage per phase (in volt) at the secondary side.Correct answer is between '263,265'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev