The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.
    Correct answer is '3.8'. Can you explain this answer?
    Verified Answer
    The maximum efficiency of a 100 kVA, signal phase transformer is 98% a...
    Since maximum efficiency occurs at 80% of full load at 0.8 P.F
    Output at ηmax = (100 × 0.8) × 0.8 = 64 kW

    ∴ Total loss = 65.3 – 64 = 1.3 kW
    This loss is divided equally between cu and iron
    ∴ Cu loss at 80% of full load = 1.3/2 = 0.65 kW
    Cu loss at full load = 0.65/82 = 1 kW

    ∴ % Regulation = [1 × 0.8 + 5 × 0.6] = 3.8%
    View all questions of this test
    Most Upvoted Answer
    The maximum efficiency of a 100 kVA, signal phase transformer is 98% a...
    Given data:
    - Power rating of transformer (S) = 100 kVA
    - Maximum efficiency (η_max) = 98%
    - Load at maximum efficiency (L_max) = 80% of full load
    - Power factor at maximum efficiency (P.F_max) = 0.8
    - Leakage impedance (Z_l) = 5%

    To find: Voltage regulation (VR) at rated load of 0.8 power factor lagging

    Formulae used:
    1. Efficiency (η) = Output power / Input power
    = Output power / (Output power + Losses)
    = S × P.F × (1 - (Z_l / Z)) / (S × P.F)

    2. Voltage regulation (VR) = (V_no-load - V_full-load) / V_full-load × 100%
    = (I_2 × Z - V_full-load) / V_full-load × 100%
    = (I_2 × Z / V_full-load - 1) × 100%
    where I_2 = rated load current, Z = impedance of transformer

    Calculations:
    1. Efficiency:
    Let's assume the voltage and current at maximum efficiency as V_max and I_max, respectively.
    P_in = V_max × I_max × P.F_max
    P_out = V_max × I_max
    Losses = P_in - P_out
    η_max = P_out / P_in = V_max × I_max / (V_max × I_max × 0.8 + Losses)
    0.98 = V_max × I_max / (V_max × I_max × 0.8 + (V_max × I_max - V_max × I_max / η_max))
    0.98 = V_max × I_max / (V_max × I_max × 0.8 + V_max × I_max - V_max × I_max / 0.98)
    V_max / V_full-load = 1 - (1 - L_max) / η_max
    V_max / V_full-load = 1 - (1 - 0.8) / 0.98
    V_max / V_full-load = 0.8163

    2. Voltage regulation:
    I_2 = S / (V_full-load × P.F)
    Z = V_full-load / (I_2 × 100 / 5) [since Z_l is given as a percentage of rated voltage]
    VR = (I_2 × Z / V_full-load - 1) × 100%
    VR = (S / (V_full-load × 0.8) × V_full-load / (I_2 × 100 / 5) / V_full-load - 1) × 100%
    VR = (S / (V_full-load × 0.8) × 20 / I_2 - 1) × 100%
    VR = (100 × 1000 / (V_full-load × 0.8) × 20 / (S / (V_full-load × 0.8))) - 1) × 100%
    VR = (100 × 1000 / (V_full-load × 0.8) × 20 / 125 - 1) × 100% [substituting S = 100 kVA]
    VR = 3.84% (approx.)

    Therefore, the voltage regulation at rated
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer?
    Question Description
    The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer?.
    Solutions for The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer?, a detailed solution for The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? has been provided alongside types of The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The maximum efficiency of a 100 kVA, signal phase transformer is 98% and occurs at 80% of full load at 0.8 P.F. If the leakage impedance of the transformer is 5%, find voltage regulation (in %) at rated load of 0.8 power factor lagging.Correct answer is '3.8'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev