Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  The two-wattmeter method is sued to measure p... Start Learning for Free
The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s are
  • a)
    6000 W and 0 W
  • b)
    5000 W and 1000 W
  • c)
    4500 W and 1500 W
  • d)
    4000 W and 2000 W
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
The two-wattmeter method is sued to measure power in 3-phase, 3-wire b...
Given that, line voltage (VL) = 400 V
Line current (IL) = 10 A
Cos ϕ = 0.866
⇒ ϕ = cos-1(0.866) = 30°
W1 = VLIL cos (30 – ϕ)
= 400 × 10 × cos (30 – 10) = 4000 W
W2 = VLIL cos (30 + ϕ)
= 400 × 10 × cos (30 + 30) = 2000 W
View all questions of this test
Most Upvoted Answer
The two-wattmeter method is sued to measure power in 3-phase, 3-wire b...
To find the readings of the two wattmeters, we first need to calculate the total power in the circuit.

Total Power = √3 * Line Voltage * Line Current * Power Factor

Total Power = √3 * 400 V * 10 A * 0.866

Total Power = 6928.2 W

Since the load power factor is lagging, the two wattmeters will give different readings. Let's assume the readings of the two wattmeters are W1 and W2.

The power measured by the first wattmeter (W1) is given by:

W1 = √3 * Line Voltage * Line Current * cos(θ)

W1 = √3 * 400 V * 10 A * cos(arccos(0.866))

W1 = 6928.2 W * 0.866

W1 = 6000 W

The power measured by the second wattmeter (W2) is given by:

W2 = √3 * Line Voltage * Line Current * cos(θ + 120°)

W2 = √3 * 400 V * 10 A * cos(arccos(0.866) + 120°)

W2 = 6928.2 W * 0.866

W2 = 6000 W

So, the readings of the two wattmeters (W1 and W2) will be 6000 W each.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer?
Question Description
The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer?.
Solutions for The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The two-wattmeter method is sued to measure power in 3-phase, 3-wire balanced inductive circuit. The line voltage and line current are 400 V and 10 A respectively. If the load power factor is 0.866 lagging, then readings of the two wattmeter’s area)6000 W and 0 Wb)5000 W and 1000 Wc)4500 W and 1500 Wd)4000 W and 2000 WCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev