The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.
    Correct answer is between '195,198'. Can you explain this answer?
    Verified Answer
    The power input in a three phase three wire delta connected balanced l...
    = 0.3592 lag
    Now capacitance is connected at the source which does not affect the active power consumption
    W = 5000 – 1000 = 4000 W
    Before connecting capacitor
    For delta Vph = VL = 440 V and IL = √3 Iph
    i.e. Iph = 8.4362 A
    ∴ Rph = Zph cos ϕ = 18.735 Ω
    Xph = Zph sin ϕ = 48.67 Ω (inductive)
    After connecting capacitor
    WA = W = 4000 W, WB = 0
    WB = VLIL cos (30 + ϕ) = 0
    30 + ϕ = 90°
    ϕ = 60°
    cos ϕ = cos 60° = 0.5 lagging
    Due to pure capacitor, Rph remain same
    Rph = 18.735 Ω
    Xcph = Xph – X'ph = 48.67 – 32.45
    = 16.2246 Ω
    = 196.1896 μF
    View all questions of this test
    Most Upvoted Answer
    The power input in a three phase three wire delta connected balanced l...
    6000 W.

    To find the total power input, we can use the formula:

    Total power = W1 + W2

    Total power = 5000 W + 6000 W

    Total power = 11000 W

    Therefore, the total power input in the three phase three wire delta connected balanced load is 11000 W.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer?
    Question Description
    The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer?.
    Solutions for The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer?, a detailed solution for The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? has been provided alongside types of The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The power input in a three phase three wire delta connected balanced load is measured by the two wattmeter method. The reading of wattmeter A is 5000 W and wattmeter B is –1000 W (with reversal of connection) if the voltage of the circuit is 440 V, 50 Hz, what is the value of capacitance (in μF) connected in delta at the source to cause the whole of the power measured by the wattmeter A only.Correct answer is between '195,198'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev