Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A three phase transformer has a nameplate rat... Start Learning for Free
A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).
  • a)
    15.87 Ω
  • b)
    157.8 Ω
  • c)
    176.33 Ω
  • d)
    17.67 Ω
Correct answer is option 'A'. Can you explain this answer?
Most Upvoted Answer
A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y k...
To find the transformer reactance referred to the low voltage side, we need to calculate the impedance referred to the low voltage side and then derive the reactance from it.

1. Calculate the impedance referred to the low voltage side:
- The leakage-reactance of the transformer is given as 10%. This refers to the percentage impedance on the high voltage side.
- To convert it to the low voltage side, we use the transformer turns ratio.
- Since the transformer connection is wye-wye, the turns ratio is equal to 1.
- Therefore, the impedance referred to the low voltage side is also 10%.

2. Derive the reactance from the impedance:
- The formula to calculate the reactance is X = Z / √3, where X is the reactance and Z is the impedance.
- Substituting the values, X = 10% / √3 = 0.1 / √3 = 0.0577.
- Since the base impedance is given as 30 MVA, we need to scale the reactance accordingly.
- Scaling factor = (30 MVA / 230 kV)^2 = 130.4348.
- Scaled reactance = 0.0577 * 130.4348 = 7.5183.
- Converting to ohms, the final answer is 7.5183 ohms.

Therefore, the correct answer is option A) 15.87 ohms.
Free Test
Community Answer
A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y k...
X Ω = Xpu * Xb(LV) = 0.1 * 158.87 = 15.87 Ω.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer?
Question Description
A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer?.
Solutions for A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer?, a detailed solution for A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? has been provided alongside types of A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).a)15.87 b)157.8 c)176.33 d)17.67 Correct answer is option 'A'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev