Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A 2 MVA, 3.3 kV, three-phase generator as the... Start Learning for Free

A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:
+ve sequence reactance, x1 = j0.10 p.u.
-ve sequence reactance, x2 = j0.10 p.u.
Zero sequence reactance, x0 = j0.05 p.u.
Reactance from neutral to ground, xn = j0.05 p.u.
The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)
  • a)
    5773.5 A
  • b)
    12371.8 A
  • c)
    14433.8 A
  • d)
    17320.5 A
Correct answer is option 'D'. Can you explain this answer?
Verified Answer
A 2 MVA, 3.3 kV, three-phase generator as the following reactance&rsqu...
The generator supplies a 3-phase, 1.5 MVA balanced passive load.
so, the system works under a base load of 1.5 MVA
The generator reactance on a base load of 1.5 MVA are as follows.
+ve sequence reactance x
-ve sequence reactance x=  
zero sequence reactance x0 = 
Reactance form neutral to ground xn
leakage reactance of transformer x
= j0.075 pu
Positive sequence network for the above system is,

X1eq = x+ xT
= j0.075 + j0.075
= j0.15 pu
Negative sequence network for above system is
X2eq = x2 + xT = j0.075 + j0.075
= j0.15 pu
Zero sequence network for above system is
X0eq = xT = j 0.075 pu
For a line to ground fault

 
= 2165.06 A
Fault current (If) = (Ib) × (If(pu))
= 2165.06 × 8
= 17320.5 A
View all questions of this test
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer?
Question Description
A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer?.
Solutions for A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer?, a detailed solution for A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 2 MVA, 3.3 kV, three-phase generator as the following reactance’s on its own base:+ve sequence reactance, x1= j0.10 p.u.-ve sequence reactance, x2= j0.10 p.u.Zero sequence reactance, x0= j0.05 p.u.Reactance from neutral to ground, xn= j0.05 p.u.The generator supplies a 3-phase, 1.5 MVA balanced passive load through a 3-phase, 2.0 MVA, 3.3 kV/400 V, delta-star transform with leakage reactance of 10%, as shown in the figure. A single-line-to-ground fault takes place at the low voltage side of the transformer. The current flowing from the transformer to the fault is (Assume base MVA is 1.5 MVA)a)5773.5 Ab)12371.8 Ac)14433.8 Ad)17320.5 ACorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev