Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  The neutral of the three phase 20 MVA, 11kV a... Start Learning for Free
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?
  • a)
    2.12 Ω
  • b)
    1.12 Ω
  • c)
    4.24 Ω
  • d)
    3.24 Ω
Correct answer is option 'A'. Can you explain this answer?
Most Upvoted Answer
The neutral of the three phase 20 MVA, 11kV alternator is earthed thro...
The minimum value of earthing resistance to protect 90% of winding can be calculated using the following formula:

R = (2/3) × (CT ratio) × (relay setting) × (neutral earthing resistance)

Where,
CT ratio = 100/5 = 20
Relay setting = 1.5 A
Neutral earthing resistance = 5 ohms

Substituting the values in the formula, we get:

R = (2/3) × 20 × 1.5 × 5
R = 40 ohms

Therefore, the minimum value of earthing resistance to protect 90% of winding is 40 ohms.
Free Test
Community Answer
The neutral of the three phase 20 MVA, 11kV alternator is earthed thro...
% winding protected = 76.4 %
resistance required to protect 90% of the winding
10 = Is*RV*100
R = 2.12 Ω.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer?
Question Description
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer?.
Solutions for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer?, a detailed solution for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? has been provided alongside types of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What should be the minimum value of the earthing resistance to protect 90% of winding?a)2.12 Ωb)1.12 Ωc)4.24 Ωd)3.24 ΩCorrect answer is option 'A'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev