The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?
  • a)
    76.4
  • b)
    77.8
  • c)
    73
  • d)
    None of the mentioned
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
The neutral of the three phase 20 MVA, 11kV alternator is earthed thro...
The given system will not protect for the LG faults, instead it will protect for earth faults.
Free Test
Community Answer
The neutral of the three phase 20 MVA, 11kV alternator is earthed thro...
To determine the percentage of the winding protected against L-G faults, we need to calculate the current flowing through the earthed resistor when there is an out of balance current of 1.5 A.

Given data:
- Three-phase alternator: 20 MVA, 11 kV
- Neutral resistance: 5 ohms
- Relay set to operate at an out of balance current of 1.5 A
- CT ratio: 100/5

First, let's calculate the out of balance current in the alternator winding:
Since the relay operates at an out of balance current of 1.5 A, the total out of balance current in the alternator winding can be calculated using the CT ratio.

Out of balance current in the winding = CT ratio × Relay operating current
= (100/5) × 1.5 A
= 30 A

Now, let's calculate the voltage across the neutral resistor:
The voltage across the neutral resistor can be calculated using Ohm's Law.

Voltage across the neutral resistor = Neutral resistance × Out of balance current
= 5 ohms × 30 A
= 150 V

To find the percentage of the winding protected against L-G faults, we need to determine the voltage across the winding during a L-G fault.

During a L-G fault, the voltage across the winding will be equal to the voltage across the neutral resistor, which is 150 V.

Now, let's calculate the percentage of the winding protected against L-G faults:

Percentage of winding protected = (Voltage across the winding during L-G fault / Line-line voltage) × 100
= (150 V / 11 kV) × 100
= 1.36%

Therefore, the correct answer is option 'D' (None of the mentioned) as none of the given options match the calculated percentage.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer?
Question Description
The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer?.
Solutions for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The neutral of the three phase 20 MVA, 11kV alternator is earthed through a resistance of 5 ohms, the relay is set to operate when there is an out of balance current of 1.5 A. The CTs have a ratio of 100/5. What percentage of the winding is protected against L-G faults?a)76.4b)77.8c)73d)None of the mentionedCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev