A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.
  • a)
    3.15 pu
  • b)
    2.37 pu
  • c)
    0.68 pu
  • d)
    4.81 pu
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has p...
The equivalent circuit for LLG fault can be drawn as:

Z1 = j0.25 pu, E = 1 pu
Z2 = j0.35 pu
Z0 = j0.10 pu

α = 1∠120°
α2 = 1∠-120°
⇒ Ib = 4.804 pu   
Free Test
Community Answer
A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has p...
Given data:
- Alternator rating: 30 MVA
- Voltage rating: 13.8 kV
- Positive sequence reactance: 0.25 pu
- Negative sequence reactance: 0.35 pu
- Zero sequence reactance: 0.10 pu
- Neutral grounding: solid grounding

To find the current in phase B during a double line to ground fault, we can use the symmetrical components method. This method allows us to analyze the fault currents in a three-phase system by breaking it down into three separate sets of single-phase circuits: positive sequence, negative sequence, and zero sequence.

1. Calculate the fault current using positive sequence components:
The positive sequence network is the same as the normal balanced three-phase system. The fault current can be calculated using the formula:

If = (3 * Vph) / (Z1 + Z0)

Where:
- If: Fault current in phase B
- Vph: Phase voltage
- Z1: Positive sequence reactance
- Z0: Zero sequence reactance

Given that Vph = 13.8 kV and Z1 = 0.25 pu, Z0 = 0.10 pu, we can substitute these values into the formula:

If = (3 * 13.8 kV) / (0.25 pu + 0.10 pu)
= (41.4 kV) / (0.35 pu)
= 118.29 kV / pu

2. Calculate the fault current using negative sequence components:
The negative sequence network represents the unbalanced condition caused by the fault. The fault current can be calculated using the formula:

In = (3 * Vph) / (Z0 + Z1)

Where:
- In: Negative sequence fault current in phase B

Given that Vph = 13.8 kV and Z0 = 0.10 pu, Z1 = 0.35 pu, we can substitute these values into the formula:

In = (3 * 13.8 kV) / (0.10 pu + 0.35 pu)
= (41.4 kV) / (0.45 pu)
= 92 kV / pu

3. Calculate the total fault current in phase B:
Since the neutral of the alternator is solidly grounded, the zero sequence fault current will also flow in phase B. The total fault current in phase B can be calculated by vectorially adding the positive, negative, and zero sequence fault currents:

I = √(If^2 + In^2 + Io^2)

Where:
- If: Positive sequence fault current
- In: Negative sequence fault current
- Io: Zero sequence fault current

Given that If = 118.29 kV / pu, In = 92 kV / pu, and Io = 0.10 pu * If, we can substitute these values into the formula:

Io = 0.10 pu * 118.29 kV / pu
= 11.83 kV

I = √((118.29 kV)^2 + (92 kV)^2 + (11.83 kV)^2)
= √(13972.1441 + 8464 + 139.7689)
= √(22476.912)
= 150.16 kV
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer?
Question Description
A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer?.
Solutions for A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A three-phase star-connected alternator rated at 30 MVA, 13.8 kV has positive, negative, and zero sequence reactance values as 0.25 pu, 0.35 pu, and 0.10 pu respectively. The neutral of the alternator is solidly grounded. Find the current in phase B when a double line to ground fault occurs on its terminals B and C.a)3.15 pub)2.37 puc)0.68 pud)4.81 puCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev