A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.
    Correct answer is between '2.7,3.2'. Can you explain this answer?
    Most Upvoted Answer
    A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It ...
    Given:
    - Synchronous generator: 30 MVA, 13.2 kV
    - Solid grounded neutral
    - Positive sequence impedance: 0.30 PU
    - Negative sequence impedance: 0.40 PU
    - Zero sequence impedance: 0.05 PU

    To find:
    - Value of reactance in the neutral to restrict fault current to rated line current for a double line to ground fault

    Solution:

    1. Find the fault current:
    The fault current for a double line to ground fault is given by the equation:
    I_fault = (V_line / (sqrt(3) * Z_seq)

    Where:
    - I_fault is the fault current
    - V_line is the line voltage
    - Z_seq is the sequence impedance

    For a double line to ground fault, the fault current is equal to the positive sequence current since the negative and zero sequence currents cancel each other out. Therefore, we can use the positive sequence impedance to calculate the fault current.

    Given:
    - Line voltage (V_line) = 13.2 kV
    - Positive sequence impedance (Z_seq) = 0.30 PU

    Substituting the values into the equation, we can calculate the fault current:
    I_fault = (13.2 kV / (sqrt(3) * 0.30 PU)

    2. Calculate the rated line current:
    The rated line current for the generator can be calculated using the formula:
    I_rated = S_rated / (sqrt(3) * V_line)

    Where:
    - I_rated is the rated line current
    - S_rated is the rated apparent power of the generator

    Given:
    - Rated apparent power (S_rated) = 30 MVA
    - Line voltage (V_line) = 13.2 kV

    Substituting the values into the equation, we can calculate the rated line current:
    I_rated = (30 MVA / (sqrt(3) * 13.2 kV)

    3. Restricting the fault current:
    To restrict the fault current to the rated line current, we need to add a reactance (X_neutral) in the neutral of the generator. The reactance value can be calculated using the formula:
    X_neutral = (V_line / I_rated) - (V_line / I_fault)

    Given:
    - Line voltage (V_line) = 13.2 kV
    - Rated line current (I_rated) = Calculated in step 2
    - Fault current (I_fault) = Calculated in step 1

    Substituting the values into the equation, we can calculate the reactance in the neutral of the generator:
    X_neutral = (13.2 kV / I_rated) - (13.2 kV / I_fault)

    The calculated value of X_neutral should be between 2.7 and 3.2 ohms to restrict the fault current to the rated line current for a double line to ground fault.
    Free Test
    Community Answer
    A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It ...
    First find rated current of generator

    Taking rated voltage and MVA as base

    Z1 = j0.30 PU, Z2 = J 0.40 PU Z0 = J 0
    Double line to ground fault

    ∴ 0.12 + 0.7 (0.05 + 3Xn) = 1.2
    Xn = 0.5 PU = 0.5 × 5.88 = 2.94 Ω 
    Explore Courses for Electrical Engineering (EE) exam

    Similar Electrical Engineering (EE) Doubts

    Top Courses for Electrical Engineering (EE)

    A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer?
    Question Description
    A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer?.
    Solutions for A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer?, a detailed solution for A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? has been provided alongside types of A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.Correct answer is between '2.7,3.2'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev