The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?
  • a)
    3200 W, 2500 W
  • b)
    3200 W, 5000 W
  • c)
    1600 W, 1250 W
  • d)
    1600 W, 5000 W
Correct answer is option 'D'. Can you explain this answer?
Most Upvoted Answer
The full-load copper loss and iron loss of a transformer are 6400 W a...
Full-load Cu loss = 6400 W
Full load iron loss = 5000 W
According to equation
where x for load, now value of x = 1/2
Cu loss depends upon load.
Iron loss = 5000 W (remains same)
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer?
Question Description
The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer?.
Solutions for The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer?, a detailed solution for The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? has been provided alongside types of The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice The full-load copper loss and iron loss of a transformer are 6400 W and 5000 W, respectively. What are the above copper loss and iron loss, respectively at half-load?a)3200 W, 2500 Wb)3200 W, 5000 Wc)1600 W, 1250 Wd)1600 W, 5000 WCorrect answer is option 'D'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev