Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  1) Two identical dc shunt generator in parall... Start Learning for Free
1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.?
Most Upvoted Answer
1) Two identical dc shunt generator in parallel to share a common load...
Problem Statement:
Two identical DC shunt generators are connected in parallel to share a common load of 500A. The armature resistance is 0.06 ohm and the no-load and terminal voltages are 265V and 250V respectively. Calculate the percentage voltage regulation (w.r.t no-load voltage) of the first generator if the second generator fails to share the load.

Solution:

Step 1: Calculate the armature current of each generator:
Since the generators are connected in parallel, the total load current is 500A. Therefore, each generator will share an equal portion of the load current.

Armature current of each generator = Total load current / Number of generators
= 500A / 2
= 250A

Step 2: Calculate the resistance drop:
Resistance drop in the armature = Armature current * Armature resistance

Resistance drop = 250A * 0.06 ohm
= 15V

Step 3: Calculate the terminal voltage of the first generator:
Terminal voltage = No-load voltage - Resistance drop

Terminal voltage of the first generator = 265V - 15V
= 250V

Step 4: Calculate the percentage voltage regulation:
Percentage voltage regulation = ((No-load voltage - Terminal voltage) / No-load voltage) * 100

Percentage voltage regulation of the first generator = ((265V - 250V) / 265V) * 100
= (15V / 265V) * 100
= 5.66%

Explanation:

When the two identical DC shunt generators are connected in parallel, they share the load current equally. In this case, each generator will share 250A of the total load current. However, when the second generator fails to share the load, the entire load current will be supplied by the first generator.

The armature resistance of the generator causes a voltage drop across it, known as the resistance drop. This drop is determined by the armature current and resistance. In this case, the resistance drop is calculated as 15V.

The terminal voltage of the first generator is the difference between the no-load voltage and the resistance drop. In this case, the terminal voltage of the first generator is calculated as 250V.

The percentage voltage regulation is calculated by comparing the difference between the no-load voltage and the terminal voltage with the no-load voltage. In this case, the percentage voltage regulation of the first generator is calculated as 5.66%.

Therefore, if the second generator fails to share the load, the terminal voltage of the first generator will be 250V, resulting in a percentage voltage regulation of 5.66% with respect to the no-load voltage of 265V.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.?
Question Description
1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.?.
Solutions for 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? defined & explained in the simplest way possible. Besides giving the explanation of 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.?, a detailed solution for 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? has been provided alongside types of 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? theory, EduRev gives you an ample number of questions to practice 1) Two identical dc shunt generator in parallel to share a common load of 500A . The armature resistance is 0.06 ohm and no-load and terminal voltages are 265 volt and 250 volt . Calculate the percentage voltage regulation (w.r.t no-load voltage) of first generator,if second generator fails to share load.? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev