Electrical Engineering (EE) Exam  >  Electrical Engineering (EE) Questions  >  A 25 kVA, 400 V, D - connected, 3-phase, cyli... Start Learning for Free
A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.
    Correct answer is between '-15,-14'. Can you explain this answer?
    Verified Answer
    A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous...
    Hint: Obtained regulation should be negative.
    View all questions of this test
    Most Upvoted Answer
    A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous...
    Given data:
    - Rated apparent power (S) = 25 kVA
    - Rated terminal voltage (Vt) = 400 V
    - Field current (If) at short-circuit condition = 5 A
    - Open-circuit voltage (Voc) at If = 5 A = 360 V
    - Power factor (pf) = 0.8 leading

    To find: Voltage regulation of the synchronous generator at rated load.

    1. Calculating the synchronous reactance (Xs):
    The synchronous reactance (Xs) can be calculated using the formula:
    Xs = Voc / If
    Substituting the given values, we get:
    Xs = 360 V / 5 A
    Xs = 72 Ω

    2. Calculating the synchronous impedance (Zs):
    The synchronous impedance (Zs) can be calculated using the formula:
    Zs = Vt / (S / √3)
    Substituting the given values, we get:
    Zs = 400 V / (25 kVA / √3)
    Zs = 400 V / (25 × 10^3 VA / √3)
    Zs = 400 V / (25 × 10^3 V / √3)
    Zs = 400 V / (25 × 10^3 V × √3)
    Zs = 0.032 Ω

    3. Calculating the synchronous reactance voltage drop (Vr):
    The synchronous reactance voltage drop (Vr) can be calculated using the formula:
    Vr = If × Xs
    Substituting the given values, we get:
    Vr = 5 A × 72 Ω
    Vr = 360 V

    4. Calculating the terminal voltage (Vt_actual):
    The actual terminal voltage (Vt_actual) can be calculated using the formula:
    Vt_actual = Vt - Vr
    Substituting the given values, we get:
    Vt_actual = 400 V - 360 V
    Vt_actual = 40 V

    5. Calculating the voltage regulation:
    The voltage regulation can be calculated using the formula:
    Voltage Regulation = (Vt - Vt_actual) / Vt × 100%
    Substituting the given values, we get:
    Voltage Regulation = (400 V - 40 V) / 400 V × 100%
    Voltage Regulation = 360 V / 400 V × 100%
    Voltage Regulation = 90%

    However, since the generator is delivering power at a leading power factor, the voltage regulation will be negative. Therefore, the correct answer is between -15% and -14%.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer?
    Question Description
    A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer?.
    Solutions for A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
    Here you can find the meaning of A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? defined & explained in the simplest way possible. Besides giving the explanation of A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer?, a detailed solution for A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? has been provided alongside types of A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? theory, EduRev gives you an ample number of questions to practice A 25 kVA, 400 V, D - connected, 3-phase, cylindrical rotor synchronous generator requires a field current of 5 A to maintain the rated armature current under short-circuit condition. For the same field current, the open-circuit voltage is 360 V. Neglecting the armature resistance and magnetic saturation, its voltage regulation (in % with respect to terminal voltage), when the generator delivers the rated load at 0.8 pf leading, at rated terminal voltage is _________.Correct answer is between '-15,-14'. Can you explain this answer? tests, examples and also practice Electrical Engineering (EE) tests.
    Explore Courses for Electrical Engineering (EE) exam

    Top Courses for Electrical Engineering (EE)

    Explore Courses
    Signup for Free!
    Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
    10M+ students study on EduRev