a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly

?
Most Upvoted Answer
a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu an...
**Calculation of Actual Resistance and Reactance Referred to HV Side**

Given data:
- Transformer rating: 4 kVA
- Primary voltage (LV side): 400 V
- Secondary voltage (HV side): 200 V
- Resistance (LV side): 0.02 pu
- Reactance (LV side): 0.06 pu

To calculate the actual resistance and reactance referred to the HV side, we need to consider the transformer's turns ratio.

**Turns Ratio Calculation:**

The turns ratio (K) is determined by the voltage ratio:

K = Vh / Vl

Where:
- K: turns ratio
- Vh: HV side voltage
- Vl: LV side voltage

Given:
- Vh = 200 V
- Vl = 400 V

Substituting the values, we get:

K = 200 / 400 = 0.5

**Resistance Referred to HV Side:**

The resistance referred to the HV side can be calculated using the turns ratio:

Rhv = Rlv / K^2

Where:
- Rhv: resistance referred to HV side
- Rlv: resistance on LV side
- K: turns ratio

Given:
- Rlv = 0.02 pu
- K = 0.5

Substituting the values, we get:

Rhv = 0.02 / (0.5^2) = 0.02 / 0.25 = 0.08 pu

Therefore, the actual resistance referred to the HV side is 0.08 pu.

**Reactance Referred to HV Side:**

The reactance referred to the HV side can also be calculated using the turns ratio:

Xhv = Xlv / K^2

Where:
- Xhv: reactance referred to HV side
- Xlv: reactance on LV side
- K: turns ratio

Given:
- Xlv = 0.06 pu
- K = 0.5

Substituting the values, we get:

Xhv = 0.06 / (0.5^2) = 0.06 / 0.25 = 0.24 pu

Therefore, the actual reactance referred to the HV side is 0.24 pu.

**Summary:**

- The actual resistance referred to the HV side is 0.08 pu.
- The actual reactance referred to the HV side is 0.24 pu.

These values are obtained by using the turns ratio to convert the resistance and reactance from the LV side to the HV side. This calculation is necessary to determine the actual values of resistance and reactance on the HV side of the transformer.
Explore Courses for Electrical Engineering (EE) exam

Similar Electrical Engineering (EE) Doubts

Top Courses for Electrical Engineering (EE)

a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly?
Question Description
a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? for Electrical Engineering (EE) 2024 is part of Electrical Engineering (EE) preparation. The Question and answers have been prepared according to the Electrical Engineering (EE) exam syllabus. Information about a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? covers all topics & solutions for Electrical Engineering (EE) 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly?.
Solutions for a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? in English & in Hindi are available as part of our courses for Electrical Engineering (EE). Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.
Here you can find the meaning of a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? defined & explained in the simplest way possible. Besides giving the explanation of a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly?, a detailed solution for a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? has been provided alongside types of a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? theory, EduRev gives you an ample number of questions to practice a 4 kva 400/200 single phase transformer has resisitance of 0.02 pu and reactance of 0.06 pu .its actual resistance and reactance refered to hv side are respectivly? tests, examples and also practice Electrical Engineering (EE) tests.
Explore Courses for Electrical Engineering (EE) exam

Top Courses for Electrical Engineering (EE)

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev