UPSC Exam  >  UPSC Questions  >  A generator rated 100 MVA, 12-6 kV has X, = ... Start Learning for Free
A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.?
Most Upvoted Answer
A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its...
Generator Specifications:
- Rated Power: 100 MVA
- Voltage Rating: 12-6 kV
- Reactance: X = X2 = 20%
- Grounding Reactance: 0.152

Fault Condition:
- Load disconnected from the system
- Double-line fault occurs at the generator terminals

Determining Sub-Transient Current:
To determine the sub-transient current in the faulted phases, we need to calculate the total fault current first. The fault current is given by the formula:

IF = E / (X + Xg)

Where:
- E is the generator voltage
- X is the generator reactance
- Xg is the grounding reactance

Calculating Fault Current:
Given that the generator is operating at its rated voltage, we can substitute the values into the formula:

IF = (12 kV) / (0.2 + 0.152)
IF = 12 kV / 0.352
IF = 34.09 kA

Calculating Sub-Transient Current:
The sub-transient current is given by the formula:

Ist = IF / X2

Substituting the values:

Ist = 34.09 kA / 0.2
Ist = 170.45 kA

Determining Line-to-Line Fault Current:
The line-to-line fault current can be calculated by multiplying the sub-transient current by a factor of √3. Therefore:

Line-to-Line Fault Current = Ist * √3
Line-to-Line Fault Current = 170.45 kA * √3
Line-to-Line Fault Current = 294.77 kA

Explanation:
- The fault condition described in the question is a double-line fault, which means that two phases are short-circuited together.
- The fault current is calculated using the formula IF = E / (X + Xg), where E is the generator voltage, X is the generator reactance, and Xg is the grounding reactance.
- The sub-transient current is then calculated using the formula Ist = IF / X2, where X2 is the sub-transient reactance.
- Finally, the line-to-line fault current is determined by multiplying the sub-transient current by a factor of √3.
- The calculated values for the sub-transient current and line-to-line fault current are 170.45 kA and 294.77 kA, respectively.
Explore Courses for UPSC exam

Top Courses for UPSC

A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.?
Question Description
A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? for UPSC 2024 is part of UPSC preparation. The Question and answers have been prepared according to the UPSC exam syllabus. Information about A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? covers all topics & solutions for UPSC 2024 Exam. Find important definitions, questions, meanings, examples, exercises and tests below for A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.?.
Solutions for A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? in English & in Hindi are available as part of our courses for UPSC. Download more important topics, notes, lectures and mock test series for UPSC Exam by signing up for free.
Here you can find the meaning of A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? defined & explained in the simplest way possible. Besides giving the explanation of A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.?, a detailed solution for A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? has been provided alongside types of A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? theory, EduRev gives you an ample number of questions to practice A generator rated 100 MVA, 12-6 kV has X, = X2 = 20% and X = 10%. Its neutral is grounded through reactance of 0 152. The generator is (b) a operating at rated voltage, load is disconnected from the system when double-line fault occurs at its terminals. Determine the sub-transient current in the faulted phases and line-to-line fault current.? tests, examples and also practice UPSC tests.
Explore Courses for UPSC exam

Top Courses for UPSC

Explore Courses
Signup for Free!
Signup to see your scores go up within 7 days! Learn & Practice with 1000+ FREE Notes, Videos & Tests.
10M+ students study on EduRev