All questions of Symmetrical and Unsymmetrical Fault Analysis for Electrical Engineering (EE) Exam

A three phase, 100 MVA, 25kV generator has solidly grounded neutral. The positive, negative, and the zero sequence reactances of the generator are 0.2 pu, 0.2 pu, and 0.05 pu, respectively, at the machine base quantities. If a bolted single phase to ground fault occurs at the terminal of the unloaded generator, the fault current in amperes immediately after the fault is________.
    Correct answer is between '15300.00,15500.00'. Can you explain this answer?

    Gate Gurus answered
    Concept:
    In a single line to ground (LG) fault, the fault current is

    Where,
    Ea = terminal voltage
    Z1 = positive sequence impedance
    Z2 = negative sequence impedance
    Z0 = zero sequence impedance
    Zn = impedance in neutral grounding
    The fault current can also be written as If = 3Ia1  
    Calculation:
    Single line to ground fault, Fault current in If = 3Ia1

    Fault current If = 15396 A.

    The zero sequence current of generator for line to ground fault is j2.4 pu. Then current through the neutral during the fault is
    • a)
      j2.4 pu
    • b)
      j0.8 pu
    • c)
      j7.2 pu
    • d)
      j0.24 pu
    Correct answer is option 'C'. Can you explain this answer?

    Gate Gurus answered
    Concept:
    In a line to ground fault, the current through the neutral during fault is given by
    If = 3Ia0
    Where Ia0 is the zero sequence current of generator
    Calculation:
    Given that, the zero sequence current of generator for line to ground fault = j2.4 pu
    The current through the neutral during the fault = 3 × j2.4 = j7.2 pu

    In a three phase system for a line to line fault the positive, negative and zero sequence voltage Va1, Va2, Va0 respectively, for phase voltage Va are related as
    • a)
      Va1 + Va2 + Va0  = Va
    • b)
      Va1 = Va2 = Va0
    • c)
      Va1 = Va2
    • d)
      Va1 + Va2 + Va0 = 0
    Correct answer is option 'C'. Can you explain this answer?

    Line to Line Fault in a Three Phase System

    A line to line fault in a three phase system occurs when two phases of the system come into contact with each other, resulting in a short circuit. This fault can cause significant damage to the electrical equipment and can lead to power outages if not addressed promptly.

    Positive, Negative, and Zero Sequence Voltages

    When a line to line fault occurs, the voltages in the three phases of the system are affected. These voltages can be represented by their positive sequence (Va1), negative sequence (Va2), and zero sequence (Va0) components.

    - The positive sequence voltage (Va1) represents the normal operating condition of the system, where the three phases are balanced and have equal magnitudes and 120-degree phase differences.
    - The negative sequence voltage (Va2) represents an unbalanced condition, where one phase has a higher magnitude than the other two phases, resulting in an unbalanced system.
    - The zero sequence voltage (Va0) represents a fault condition, where all three phases have equal magnitudes and zero phase difference.

    Relation between Positive, Negative, and Zero Sequence Voltages

    In a line to line fault, the positive, negative, and zero sequence voltages are related as follows:

    Va1 = Va2 = Va0

    This means that during a line to line fault, all three sequence voltages have the same magnitude and phase. This is because the fault condition causes the system to become symmetrical, with all three phases experiencing the same fault current.

    Explanation of the Correct Answer (Option C)

    The correct answer to the given question is option C, which states that Va1 = Va2 = Va0. This means that during a line to line fault, all three sequence voltages have the same magnitude and phase.

    This is consistent with the behavior observed during a line to line fault, where the fault current flows equally through all three phases. As a result, the voltages across the faulted phases become equal, leading to the equality of the positive, negative, and zero sequence voltages.

    Therefore, option C is the correct answer as it accurately describes the relationship between the positive, negative, and zero sequence voltages in a three phase system during a line to line fault.

    In which type of fault, zero sequence currents do not exist?
    • a)
      Line to Line
    • b)
      Line-Line to Ground
    • c)
      Line to Ground
    • d)
      Line-Line-Line to Ground
    Correct answer is option 'A'. Can you explain this answer?

    Pooja Patel answered
    Line to Line fault:

    When two conductors of a 3-phase system are short-circuited line to line fault occurs.
    IR = 0
    IF = IY = -IB

    From equation (i), we found that zero sequence currents do not exist in the LL fault.

    The most common type of fault is
    • a)
      single phase to ground
    • b)
      phase-to-phase
    • c)
      three phase to ground
    • d)
      two phase to ground
    Correct answer is option 'A'. Can you explain this answer?

    Single Phase to Ground Fault
    Single phase to ground fault is the most common type of fault in electrical systems. This fault occurs when one of the conductors comes into contact with the ground or a grounded surface.

    Causes of Single Phase to Ground Fault
    - Insulation breakdown: Insulation failure can lead to a direct contact between a conductor and the ground, causing a fault.
    - Equipment failure: Malfunctioning equipment or damaged cables can also result in a single phase to ground fault.
    - Environmental factors: Environmental conditions such as lightning strikes or moisture can cause faults as well.

    Effects of Single Phase to Ground Fault
    - Uneven distribution of current: In a single phase to ground fault, the faulted phase carries more current compared to the other phases.
    - Voltage imbalance: The fault can cause voltage imbalances in the system, affecting the performance of connected equipment.
    - Fire hazard: If not detected and cleared promptly, a single phase to ground fault can lead to overheating and potentially start a fire.

    Detection and Protection
    - Ground fault protection devices: Ground fault circuit interrupters (GFCIs) are commonly used to detect and protect against single phase to ground faults.
    - Insulation monitoring: Periodic insulation resistance tests can help identify potential faults before they occur.
    - Monitoring systems: Advanced monitoring systems can provide real-time alerts and notifications in case of a fault.
    In conclusion, single phase to ground faults are a common issue in electrical systems and can have serious consequences if not addressed promptly. Proper detection, protection, and maintenance measures are essential to ensure the safety and reliability of the system.

    Single phase to ground fault is a/an ______ fault.
    • a)
      unsymmetrical
    • b)
      disaster
    • c)
      thermal
    • d)
      symmetrical
    Correct answer is option 'A'. Can you explain this answer?

    Gate Gurus answered
    Single line-to-ground fault:
    On a transmission line when one conductor drops to the ground or comes in contact with the neutral conductor, then there is an insulation breakdown between one of the phases and earth, due to which single line to ground fault takes place. Such types of failures may occur in a power system due to many reasons like high-speed wind, falling off a tree, lightning, etc.
    Unsymmetrical faults: 
    These are faults that lead to unequal currents with unequal phase shifts in a three-phase system. The unsymmetrical fault occurs in a system due to the presence of an open circuit or short circuit of transmission or distribution line. These are classified as
    • Single line to ground fault (LG)
    • Double line fault (LL)
    • Double line to ground fault (LLG)

    In case of single line to ground fault
    • a)
      All sequence networks are connected in parallel
    • b)
      All sequence networks are connected in series
    • c)
      Positive and negative sequence networks are connected in parallel
    • d)
      Zero and negative sequence networks are connected in series
    Correct answer is option 'B'. Can you explain this answer?

    Zoya Sharma answered
    The following circuit shown is a system with a line to ground fault.

    Here, Va = 0, Ib = 0, Ic = 0

    By substituting Ib and Ic values,

    Hence in LG faults, all of the three components la0, la1, and la2 are equal.
    Va = 0 = Va1 + Va2 + Va0
    Now substituting the values of Va0, Va1 and Va2 from the sequence network equation,
    Ea – Ia1Z1 – Ia2Z2 – Ia0Z0 = 0
    ⇒ Ea – Ia1Z1 – Ia1Z2 – Ia1Z0 = 0

    From the above equation, it is clear that to simulate an L-G fault all the three sequence networks are required and since the currents are equal in magnitude and phase angle, the three sequence networks must be connected in series. The voltage across each sequence network corresponds to the same sequence component of Va.
    The interconnection of the sequence network is shown in the figure.

    Determine the fault current in the system following a double line to ground short circuit fault at the terminal of a star connected synchronous generator operating initially on an open circuit voltage of 1.0 pu. The positive, negative, and zero sequences reactance of the generator are, respectively j0.35, j0.25, and j0.20, and the star point is isolated from the ground.
    • a)
      -2.165 pu
    • b)
      -2.887 pu
    • c)
      -3.75 pu
    • d)
      -5 pu
    Correct answer is option 'B'. Can you explain this answer?

    Srestha Kumar answered
    To determine the fault current in the system following a double line to ground short circuit fault at the terminal of a star-connected synchronous generator, we need to calculate the positive sequence fault current (I1), negative sequence fault current (I2), and zero sequence fault current (I0) separately.

    Positive Sequence Fault Current (I1):
    The positive sequence fault current is calculated using the formula:

    I1 = Vf / (Z1 + Z0)

    Where,
    Vf = Fault voltage (1.0 pu)
    Z1 = Positive sequence reactance (j0.35 pu)
    Z0 = Zero sequence reactance (j0.20 pu)

    Substituting the given values, we get:

    I1 = 1.0 / (j0.35 + j0.20)

    To simplify the calculation, we can convert the reactances into admittances:

    Y1 = 1 / Z1 = 1 / (j0.35) = -j2.857
    Y0 = 1 / Z0 = 1 / (j0.20) = -j5.0

    Now, we can rewrite the formula for I1 as:

    I1 = Vf * (Y1 + Y0)

    Substituting the values, we get:

    I1 = 1.0 * (-j2.857 - j5.0)
    = -j2.857 - j5.0
    = -j7.857

    Negative Sequence Fault Current (I2):
    The negative sequence fault current is calculated using the formula:

    I2 = Vf / (Z2 + Z0)

    Where,
    Z2 = Negative sequence reactance (j0.25 pu)

    Substituting the given values, we get:

    I2 = 1.0 / (j0.25 + j0.20)
    = 1.0 / (j0.45)
    = -j2.222

    Zero Sequence Fault Current (I0):
    Since the star point is isolated from the ground, there is no zero sequence path. Therefore, the zero sequence fault current is zero (0).

    Overall Fault Current:
    The overall fault current is the vector sum of the positive, negative, and zero sequence fault currents. Since the zero sequence fault current is zero (0), the overall fault current is equal to the positive sequence fault current:

    Overall Fault Current = I1 = -j7.857

    Therefore, the fault current in the system following a double line to ground short circuit fault at the terminal of the star-connected synchronous generator is -j7.857 pu.

    Possible faults may occur on a transmission line are
    1. 3-phase fault
    2. L-L-G fault
    3. L-L fault
    4. L-G fault
    The decreasing order of severity of the faults from the stability point of view is:
    • a)
      1-2-3-4
    • b)
      1-4-3-2
    • c)
      1-3-2-4
    • d)
      1-3-4-2
    Correct answer is option 'A'. Can you explain this answer?

    Shivani Saha answered
    Fault Severity in Transmission Line

    When a fault occurs on a transmission line, it can lead to a disruption in the power flow and stability of the system. The severity of the fault depends on various factors such as fault type, fault impedance, fault location, and the characteristics of the power system.

    In this question, we are given four possible faults that can occur on a transmission line: 3-phase fault, L-L-G fault, L-L fault, and L-G fault. We need to determine the decreasing order of severity of these faults from a stability point of view.

    Explanation:

    To determine the order of fault severity, we need to consider the impact of each fault on the stability of the power system. The stability of a power system refers to its ability to maintain synchronous operation under normal and abnormal conditions.

    1. 3-phase fault: A 3-phase fault is the most severe type of fault as it involves a complete short circuit between all three phases. This fault can cause a rapid increase in fault current and can lead to severe damage to the equipment. It can also result in a large transient disturbance in the system and can cause the system to become unstable. Therefore, 3-phase fault has the highest severity.

    2. L-L-G fault: A L-L-G fault is a fault between two phases with a ground connection. This fault can also lead to a significant fault current, but it is less severe than a 3-phase fault. The presence of the ground connection can limit the fault current and reduce the impact on the stability of the system. Therefore, L-L-G fault has a lower severity compared to a 3-phase fault.

    3. L-L fault: A L-L fault refers to a fault between two phases without any ground connection. This fault can result in a high fault current, but it is less severe than a L-L-G fault. The absence of a ground connection can limit the fault current to some extent and reduce the impact on the stability of the system. Therefore, L-L fault has a lower severity compared to a L-L-G fault.

    4. L-G fault: A L-G fault is the least severe type of fault among the given options. It involves a fault between one phase and ground. The fault current in this case is limited by the ground impedance, which is typically higher than the line impedance. As a result, the impact on the stability of the system is relatively lower compared to the other fault types. Therefore, L-G fault has the lowest severity among the given options.

    Conclusion:

    Based on the above analysis, the decreasing order of severity of the faults from a stability point of view is:
    a) 3-phase fault
    b) L-L-G fault
    c) L-L fault
    d) L-G fault

    Therefore, the correct answer is option 'A'.

    For a fault at terminals of a synchronous generator, the fault current is maximum for a
    • a)
      3 phase fault
    • b)
      3 phase to ground fault
    • c)
      Line to ground fault
    • d)
      Line to Line fault
    Correct answer is option 'C'. Can you explain this answer?

    Poulomi Chopra answered
    Line to ground fault results in maximum fault current in a synchronous generator. This can be explained by considering the fault conditions and the characteristics of the generator.

    1. Fault Conditions:
    - In a synchronous generator, the stator winding is connected to the grid or the power system, while the rotor winding is connected to a DC source.
    - When a fault occurs in the generator, it creates a low-impedance path for the fault current to flow.
    - The fault current depends on the fault impedance and the voltage source behind the generator.

    2. Fault Impedance:
    - The fault impedance in a line to ground fault is lower compared to other fault types.
    - In a line to ground fault, one of the phase conductors comes into contact with the ground or a low-impedance path is formed between one phase and the ground.
    - This results in a direct short circuit between one phase and the ground, offering the lowest impedance path for the fault current.

    3. Generator Characteristics:
    - Synchronous generators have a high short-circuit current capability due to the presence of a strong magnetic field in the rotor.
    - The fault current depends on the voltage magnitude behind the generator and the fault impedance.
    - In the case of a line to ground fault, the fault impedance is significantly lower, leading to a higher fault current.
    - The fault current is further amplified by the high voltage magnitude behind the generator, which pushes more current into the fault.

    In summary, line to ground fault results in the maximum fault current in a synchronous generator due to the low fault impedance and the high voltage magnitude behind the generator. This fault type offers a direct short circuit path between one phase and the ground, causing a significant increase in fault current compared to other fault types.

    Find the base impedance for a 10 kV, 10 MVA 3-Phase system
    • a)
      5 ohms
    • b)
      7 ohms
    • c)
      10 ohms
    • d)
      1 kilo ohms
    Correct answer is option 'C'. Can you explain this answer?

    Base Impedance Calculation for a 3-Phase System

    To calculate the base impedance for a 3-phase system, we need to use the following formula:

    Zbase = Vbase^2 / Sbase

    Where,
    Vbase = Phase-to-phase voltage of the system
    Sbase = Apparent power of the system

    Given data:
    Phase-to-phase voltage, V = 10 kV
    Apparent power, S = 10 MVA

    Step 1: Calculate the base apparent power (Sbase)
    Sbase = 10 MVA / 3
    Sbase = 3.33 MVA

    Step 2: Calculate the base voltage (Vbase)
    Vbase = 10 kV / √3
    Vbase = 5.77 kV

    Step 3: Calculate the base impedance (Zbase)
    Zbase = Vbase^2 / Sbase
    Zbase = (5.77 kV)^2 / 3.33 MVA
    Zbase = 10 ohms

    Therefore, the correct answer is option (c) 10 ohms.

    Irrespective of the causes, which is the fault in a 3-phase system?
    • a)
      Unsymmetrical faults
    • b)
      Both Symmetrical faults and Unsymmetrical faults
    • c)
      Symmetrical faults
    • d)
      External faults
    Correct answer is option 'B'. Can you explain this answer?

    **Faults in a 3-Phase System**

    A fault in a 3-phase system refers to an abnormal condition that occurs when there is a failure or malfunction in the electrical network. These faults can be caused by various factors such as short circuits, ground faults, insulation breakdown, or equipment failure. Regardless of the causes, faults in a 3-phase system can be categorized into two types: symmetrical faults and unsymmetrical faults.

    **Symmetrical Faults**

    Symmetrical faults occur when all three phases of the system experience a fault of the same magnitude and at the same time. This can happen due to a short circuit between all three phases or a fault to ground that affects all three phases equally. Symmetrical faults are characterized by balanced voltages and currents, and they can cause severe damage to the equipment and electrical network. However, they are relatively easy to detect and analyze, as the fault currents and voltages are symmetrical.

    **Unsymmetrical Faults**

    Unsymmetrical faults, on the other hand, occur when the fault affects one or two phases of the system, while the remaining phases remain unaffected. This can happen due to a short circuit between two phases, a fault to ground on one phase, or a combination of faults. Unsymmetrical faults are characterized by unbalanced voltages and currents, and they can be more challenging to detect and analyze compared to symmetrical faults. The severity and impact of unsymmetrical faults depend on the type and location of the fault.

    **The Fault in a 3-Phase System**

    The fault in a 3-phase system refers to any abnormal condition that disrupts the normal operation of the electrical network. Regardless of the causes, both symmetrical faults and unsymmetrical faults can cause faults in a 3-phase system. Therefore, the correct answer to the question is option 'B' - Both symmetrical faults and unsymmetrical faults.

    It is important to note that external faults, such as faults occurring in the power supply or in connected equipment, can also cause faults in a 3-phase system. These external faults can be either symmetrical or unsymmetrical, depending on the nature of the fault. Therefore, option 'D' - External faults, cannot be considered as the only fault in a 3-phase system.

    In conclusion, faults in a 3-phase system can be both symmetrical and unsymmetrical in nature, and they can be caused by various factors. It is important for electrical engineers and technicians to be able to detect, analyze, and mitigate these faults to ensure the safety and reliability of the electrical network.

    Line-to-ground fault occurs:
    • a)
      Due to short circuit between two conductors
    • b)
      Due to insulation breakdown between one of the phase and earth
    • c)
      Due to the breakdown of insulation between two phases and simultaneous breakdown of insulation between the third phase and earth
    • d)
      Due to fault breakdowns of insulation between two phases and earth occur
    Correct answer is option 'B'. Can you explain this answer?

    Aman Datta answered
    Line-to-ground fault occurs due to insulation breakdown between one of the phase and earth.

    Explanation:

    A line-to-ground fault is a fault condition in an electrical system where there is a breakdown of insulation between one of the phases and the earth. This fault can occur in different types of electrical systems, including power distribution systems, industrial systems, and residential electrical systems.

    Causes of Line-to-Ground Fault:

    - Insulation breakdown: The most common cause of a line-to-ground fault is insulation breakdown. Insulation is used to prevent the flow of current between conductors and between conductors and the earth. When the insulation fails or breaks down, it allows current to flow between the phase conductor and the earth, resulting in a fault.

    Effects of Line-to-Ground Fault:

    - Current flow: When a line-to-ground fault occurs, current flows from the phase conductor to the earth. This can result in a significant increase in current, which can cause overheating of equipment and conductors.

    - Voltage drop: The fault current flowing through the faulted phase conductor causes a voltage drop. This can affect the voltage levels in the system and may result in a decrease in voltage at the fault location.

    - Ground potential rise: A line-to-ground fault can also cause a rise in the ground potential around the fault location. This can be dangerous as it can create a difference in potential between different parts of the ground, leading to electric shock hazards.

    Protection and Fault Clearing:

    - Ground fault protection: In order to protect against line-to-ground faults, ground fault protection devices are used. These devices detect the fault current and quickly disconnect the faulty circuit from the power supply. This helps to minimize the damage caused by the fault and prevent further hazards.

    - Fault clearing: Once a line-to-ground fault is detected, it is important to clear the fault as quickly as possible. This is typically done by isolating the faulted circuit and repairing or replacing the faulty equipment or insulation.

    In conclusion, a line-to-ground fault occurs due to insulation breakdown between one of the phase conductors and the earth. This fault can cause current flow, voltage drop, and ground potential rise. Proper protection and fault clearing measures are necessary to prevent damage and hazards associated with line-to-ground faults.

    A 30 MVA, 13.2 KV synchronous generator has solid grounded neural. It positive, negative and zero sequence impedance are 0.30, 0.40 and 0.05 PU respectively. What value of reactance (in ohm) must be placed in the neutral of the generator to restrict the fault current to ground to rated line current for a double line to ground fault.
      Correct answer is between '2.7,3.2'. Can you explain this answer?

      Rajesh Saha answered
      Given:
      - Synchronous generator: 30 MVA, 13.2 kV
      - Solid grounded neutral
      - Positive sequence impedance: 0.30 PU
      - Negative sequence impedance: 0.40 PU
      - Zero sequence impedance: 0.05 PU

      To find:
      - Value of reactance in the neutral to restrict fault current to rated line current for a double line to ground fault

      Solution:

      1. Find the fault current:
      The fault current for a double line to ground fault is given by the equation:
      I_fault = (V_line / (sqrt(3) * Z_seq)

      Where:
      - I_fault is the fault current
      - V_line is the line voltage
      - Z_seq is the sequence impedance

      For a double line to ground fault, the fault current is equal to the positive sequence current since the negative and zero sequence currents cancel each other out. Therefore, we can use the positive sequence impedance to calculate the fault current.

      Given:
      - Line voltage (V_line) = 13.2 kV
      - Positive sequence impedance (Z_seq) = 0.30 PU

      Substituting the values into the equation, we can calculate the fault current:
      I_fault = (13.2 kV / (sqrt(3) * 0.30 PU)

      2. Calculate the rated line current:
      The rated line current for the generator can be calculated using the formula:
      I_rated = S_rated / (sqrt(3) * V_line)

      Where:
      - I_rated is the rated line current
      - S_rated is the rated apparent power of the generator

      Given:
      - Rated apparent power (S_rated) = 30 MVA
      - Line voltage (V_line) = 13.2 kV

      Substituting the values into the equation, we can calculate the rated line current:
      I_rated = (30 MVA / (sqrt(3) * 13.2 kV)

      3. Restricting the fault current:
      To restrict the fault current to the rated line current, we need to add a reactance (X_neutral) in the neutral of the generator. The reactance value can be calculated using the formula:
      X_neutral = (V_line / I_rated) - (V_line / I_fault)

      Given:
      - Line voltage (V_line) = 13.2 kV
      - Rated line current (I_rated) = Calculated in step 2
      - Fault current (I_fault) = Calculated in step 1

      Substituting the values into the equation, we can calculate the reactance in the neutral of the generator:
      X_neutral = (13.2 kV / I_rated) - (13.2 kV / I_fault)

      The calculated value of X_neutral should be between 2.7 and 3.2 ohms to restrict the fault current to the rated line current for a double line to ground fault.

      What will the zero-sequence current when line to ground fault occurs and the current in faulted phase is 300 A?
      • a)
        100 A
      • b)
        300 A
      • c)
        50 A
      • d)
        150 A
      Correct answer is option 'A'. Can you explain this answer?

      Zoya Sharma answered
      Zero sequence current in LG fault
      For LG fault, all the sequence currents are equal.

      Where
      IR0 is the zero-sequence current
      if is the fault current

      Per unit impedance is equal to
      • a)
        base impedance / actual impedance
      • b)
        actual impedance / base impedance
      • c)
        base MVA / base current
      • d)
        base current / base MVA
      Correct answer is option 'B'. Can you explain this answer?

      Pooja Patel answered
      Per unit value of a quantity is defined as the ratio of its actual value to its base value.
      Per unit impedance = actual impedance / base impedance
      Important Point:
      The relation between new per-unit value & old per unit value impedance


      Where,
      (Zpu)new = New per unit value of impedance
      (Zpu)old = Old per unit value of impedance
      kVbase = Old base value of voltage
      kVnew = New base value of voltage
      MVAnew = New base value of power
      MVAold = Old base value of power

      On which among the following factors does the magnitude of the fault current depend?
      • a)
        Total impedance up to the fault
      • b)
        Voltage at the fault point
      • c)
        Both (a) and (b)
      • d)
        None of these
      Correct answer is option 'C'. Can you explain this answer?

      Pooja Patel answered
      The amount of current that will flow through a short circuit depends on two values:
      • The system voltage
      • The connected total impedance of the path from the source to the point of the fault.​
      • This impedance normally includes the feeder conductor’s resistance and reactance, any transformers, impedances (going from the point of fault back to the energy source), and any other equipment connected in the path of current flow.

      A 25 MVA, 33 kV transformer has a pu impedance of 0.9. The pu impedance at a new base 50 MVA at 11 kV would be
      • a)
        10.4
      • b)
        12.2
      • c)
        14.4
      • d)
        16.2
      Correct answer is option 'D'. Can you explain this answer?

      Pooja Patel answered
      25 MVA, 33 kV transformer – Zpu old = 0.9, MVAold = 25 MVA, Vold = 33 kV
      At new base, Pnew = 50 MVA, Vnew = 11kV
      As Zpu = Z/Zbase
      = 0.9 × 2 × 9
      Zpu new = 16.2 pu

      What is the main purpose of reactance diagram?
      • a)
        Load flow analysis
      • b)
        Falt analysis
      • c)
        Calculation of ratings of Alternators
      • d)
        Calculation of ratings of Transformers
      Correct answer is option 'B'. Can you explain this answer?

      Jyoti Basak answered
      The main purpose of a reactance diagram is to analyze faults in electrical power systems. Reactance diagrams are used in fault analysis to determine various parameters related to the fault, such as fault currents, fault impedance, and fault locations. This information is crucial in designing protective devices and ensuring the safety and reliability of the power system.

      Here is a detailed explanation of why the main purpose of a reactance diagram is fault analysis:

      1. Fault Analysis:
      - Faults are abnormal conditions that occur in power systems, such as short circuits or ground faults. These faults can lead to equipment damage, power outages, or even electrical accidents.
      - Fault analysis involves studying the behavior of the power system during these faults and determining the appropriate actions to mitigate their effects.
      - A reactance diagram is a graphical representation of the reactances (inductance and capacitance) of various components in a power system, such as generators, transformers, transmission lines, and loads.
      - By using reactance diagrams, engineers can analyze the behavior of the power system during faults and calculate important parameters related to the fault.

      2. Fault Current Calculation:
      - During a fault, high currents flow through the system. These fault currents need to be accurately calculated to ensure the proper coordination and operation of protective devices, such as circuit breakers and relays.
      - Reactance diagrams help in determining the fault current magnitude and direction by considering the reactances of the different components in the system.
      - By analyzing the reactance diagram, engineers can calculate the fault current and use this information to properly size protective devices and ensure the safety of the system.

      3. Fault Impedance Calculation:
      - Fault impedance is the total impedance seen by the fault current during a fault. It is the combination of the impedance of the faulted component and the reactances of the other system components.
      - Reactance diagrams assist in calculating the fault impedance by considering the reactances of various components.
      - Fault impedance is an important parameter in fault analysis as it helps in determining the fault current magnitude and fault voltage levels at different locations in the system.

      4. Fault Location:
      - Fault location is the process of determining the exact location of the fault in the power system.
      - Reactance diagrams are utilized to estimate the fault location by analyzing the changes in current and voltage magnitudes along the transmission lines and other components.
      - By using reactance diagrams, engineers can identify the section of the power system where the fault has occurred, facilitating faster fault detection and restoration.

      In summary, the main purpose of a reactance diagram is fault analysis. It helps in calculating fault currents, fault impedances, and fault locations, which are crucial for the proper design and operation of protective devices in electrical power systems.

      The per unit impedance Z(Pu) in 3 - phase system is 
      • a)
      • b)
      • c)
      • d)
      Correct answer is option 'A'. Can you explain this answer?

      Per unit quantity:
      Per unit quantity = Actual quantity in the units / Base (or) reference quantity in the same units
      ⇒ Per unit impedance Zpu = Zactual / Zbase
      ⇒ Zpu = ZΩ × MVAb / (kVb)2
      Conversion of one per unit impedance into another per unit impedance is given by

      Symmetrical fault currents are restricted by
      • a)
        System impedance
      • b)
        System voltage profile
      • c)
        System power rating
      • d)
        D.C. component of fault current
      Correct answer is option 'A'. Can you explain this answer?

      Rajesh Kumar answered
      Explanation:

      System Impedance:
      Symmetrical fault currents are restricted by system impedance. The impedance of the system determines how much current will flow in the event of a fault. Higher system impedance will limit the fault current magnitude, providing a level of protection to the system.

      Role of System Impedance:
      - When a fault occurs in a power system, the fault current magnitude is determined by the system impedance.
      - The higher the impedance, the lower the fault current magnitude.
      - System impedance acts as a natural limiter for fault currents, preventing excessive current flow that can potentially damage equipment and pose safety hazards.

      Impedance Matching:
      - Matching system impedance to the designed level helps in controlling fault currents and ensuring the stability of the power system.
      - Proper impedance coordination in the system design helps in limiting fault currents within safe levels.

      Importance of Restricting Symmetrical Fault Currents:
      - Restricting symmetrical fault currents is crucial for protecting equipment, minimizing damage, and ensuring the safety of personnel.
      - High fault currents can lead to equipment failure, thermal damage, and even fire hazards.
      - By limiting fault currents through system impedance, the overall reliability and stability of the power system are enhanced.
      In conclusion, system impedance plays a significant role in restricting symmetrical fault currents in a power system. By understanding and appropriately managing system impedance, engineers can ensure the safety and reliability of the electrical infrastructure.

      The per unit impedance of a circuit element is x. If the base kV and base MVA are doubled, then the new value of the per unit impedance of the circuit element is
      • a)
        x
      • b)
        x/2
      • c)
        2x
      • d)
        x/4
      Correct answer is option 'B'. Can you explain this answer?

      Gargi Mishra answered
      Explanation:

      Per unit impedance is a way of representing impedances in a circuit on a common base. The per unit impedance of a circuit element is defined as the ratio of the actual impedance of the element to a base impedance.

      Let the base kV and base MVA be denoted by Vb and Sb respectively. Let the actual impedance of the circuit element be denoted by Z.

      Then, the per unit impedance of the circuit element is given by:

      Zpu = (Z / Vb^2) / (Sb / 1000)

      where Zpu is the per unit impedance.

      If the base kV and base MVA are doubled, then the new base kV and base MVA become 2Vb and 2Sb respectively.

      The new per unit impedance of the circuit element can be calculated using the same formula as before but with the new base values:

      Zpu' = (Z / (2Vb)^2) / (2Sb / 1000)

      Simplifying this expression, we get:

      Zpu' = Zpu / 4

      Therefore, the new value of the per unit impedance of the circuit element is x/2, which corresponds to option B.

      Conclusion:

      When the base kV and base MVA are doubled, the new value of the per unit impedance of the circuit element is equal to the original per unit impedance divided by 4.

      Which of the following depicts Per-unit value of a quantity?
      • a)
        Ratio of Actual quantity in any unit to Base or reference value of quantity in the same unit
      • b)
        Ratio of Base of reference value of quantity in the same unit to Actual quantity in any unit
      • c)
        Half of the Actual quantity in any unit
      • d)
        Twice of the Actual quantity in any unit
      Correct answer is option 'A'. Can you explain this answer?

      Per-unit value of a quantity:
      Per-unit value of a quantity is defined as the ratio of the actual quantity in any unit to the base or reference value of the quantity in the same unit. It is commonly used in power systems and electrical engineering to normalize values for comparison and analysis.

      Explanation:
      - The per-unit system is a method used to express and compare electrical quantities like voltage, current, power, and impedance in power systems.
      - It helps in simplifying calculations and eliminating the need to deal with different units of measurement.
      - By expressing values in per-unit, engineers can easily compare system components regardless of their actual rating.

      Example:
      - If the base or reference value for a voltage quantity is 100 V, and the actual voltage is 120 V, then the per-unit value of voltage would be 1.2 (120 V / 100 V).
      Therefore, the correct depiction of the per-unit value of a quantity is option 'A' - the ratio of the actual quantity in any unit to the base or reference value of the quantity in the same unit.

      A synchronous generator is rated at 40 MVA, 14.6 kV and 50 Hz. The base impedance of the generator will be
      • a)
        5.33 Ω
      • b)
        6.29 Ω
      • c)
        3.57 Ω
      • d)
        7.25 Ω
      Correct answer is option 'A'. Can you explain this answer?

      Understanding Base Impedance
      In electrical engineering, base impedance is a reference value used in per-unit system calculations, which simplifies the analysis of power systems. It is calculated using the rated power (S) and rated voltage (V) of the generator.

      Formula for Base Impedance
      The base impedance (Z_base) can be calculated using the formula:
      \[
      Z_{base} = \frac{V_{base}^2}{S_{base}}
      \]
      Where:
      - \( V_{base} \) is the base voltage in volts (V)
      - \( S_{base} \) is the base power in volt-amperes (VA)

      Given Values
      For the synchronous generator:
      - Rated Power \( S = 40 \, \text{MVA} = 40 \times 10^6 \, \text{VA} \)
      - Rated Voltage \( V = 14.6 \, \text{kV} = 14.6 \times 10^3 \, \text{V} \)

      Calculation Steps
      1. **Convert base voltage to volts**:
      \( V_{base} = 14.6 \times 10^3 \, \text{V} = 14600 \, \text{V} \)
      2. **Calculate base impedance**:
      \[
      Z_{base} = \frac{(14600)^2}{40 \times 10^6}
      \]
      3. **Perform the calculation**:
      - \( (14600)^2 = 213160000 \)
      - \( Z_{base} = \frac{213160000}{40000000} = 5.33 \, \Omega \)

      Conclusion
      Thus, the base impedance of the synchronous generator is \( 5.33 \, \Omega \), confirming that the correct answer is option 'A'.

      The reactance data for a power system is shown in the figure in per unit on a common base is as follows.
      G1: X1 = X2 = j0.1, X0 = j0.05
      G2: X1 = X2 = j0.1, X0 = j0.05
      T1: X1 = X2 = j0.25, X0 = j0.25
      T2: X1 = X2 = j0.25, X0 = j0.25
      Line: X1 = X2 = j0.3, X0 = j0.5
      If a double line to ground fault occurs at bus 1, the fault current is _______
      • a)
        4.39 pu
      • b)
        4.67 pu
      • c)
        3.87 pu
      • d)
        4.98 pu
      Correct answer is option 'D'. Can you explain this answer?

      For the given power system network, the positive sequence impedance network is given below.

      The impedance at a point of fault is,
      X1eq = (j0.35)∥(j0.65) 
      = j0.2275 pu
      Negative sequence reactance is the same as positive sequence reactance
      X2eq = X1eq = j0.2275pu 
      The zero sequence reactance network is,

      Zero sequence impedance
      Z0eq = j0.25 ∥ j0.75 = j0.1875 pu
      For a double line to fault at bus 1 is,

      Impedance diagram is used for analysis of __________
      • a)
        Load flow
      • b)
        Alternator
      • c)
        Fault
      • d)
        Transmission Line
      Correct answer is option 'A'. Can you explain this answer?

      Pooja Patel answered
      Impidance diagram is made for the analysis of load flow. Fault analysis is doen by the help of reactance diagram. All these diagrams are made using symmetrical component analysis method on per phase basis.

      Calculate the per-unit synchronous reactance on the base value of 200 MVA and 20 kV when a 100 MVA with 20 kV synchronous generator has 1pu synchronous reactance.
      • a)
        2 pu
      • b)
        4 pu
      • c)
        6 pu
      • d)
        8 pu
      Correct answer is option 'A'. Can you explain this answer?

      Sarthak Yadav answered

      Calculation of Per-Unit Synchronous Reactance:

      - Given Base Values:
      - S_base = 200 MVA
      - V_base = 20 kV

      - Given Generator Rating:
      - S_gen = 100 MVA
      - V_gen = 20 kV
      - Xd = 1 pu

      Step 1: Calculate the Base Current (I_base):
      I_base = S_base / (sqrt(3) * V_base)
      I_base = 200 MVA / (sqrt(3) * 20 kV) = 5.7735 kA

      Step 2: Calculate the Base Impedance (Z_base):
      Z_base = V_base^2 / S_base
      Z_base = (20 kV)^2 / 200 MVA = 2 ohms

      Step 3: Calculate the Actual Synchronous Reactance (X_d_actual):
      X_d_actual = X_d * Z_base
      X_d_actual = 1 pu * 2 ohms = 2 ohms

      Step 4: Calculate the Per-Unit Synchronous Reactance (X_d_pu):
      X_d_pu = X_d_actual / Z_base
      X_d_pu = 2 ohms / 2 ohms = 1 pu

      Therefore, the per-unit synchronous reactance on the base value of 200 MVA and 20 kV when a 100 MVA with 20 kV synchronous generator has 1 pu synchronous reactance is 2 pu. The correct answer is option 'A'.

      A three phase transformer has a nameplate rating of 30 MVA, 230Y/69Y kV with a leakage-reactance of 10% and the transformer connection is wye-wye. Choosing a base of 30MVA and 230 kV on high voltage side, the transformer reactance referred to the low voltage side will be _______(in ohms).
      • a)
        15.87 Ω
      • b)
        157.8 Ω
      • c)
        176.33 Ω
      • d)
        17.67 Ω
      Correct answer is option 'A'. Can you explain this answer?

      To find the transformer reactance referred to the low voltage side, we need to calculate the impedance referred to the low voltage side and then derive the reactance from it.

      1. Calculate the impedance referred to the low voltage side:
      - The leakage-reactance of the transformer is given as 10%. This refers to the percentage impedance on the high voltage side.
      - To convert it to the low voltage side, we use the transformer turns ratio.
      - Since the transformer connection is wye-wye, the turns ratio is equal to 1.
      - Therefore, the impedance referred to the low voltage side is also 10%.

      2. Derive the reactance from the impedance:
      - The formula to calculate the reactance is X = Z / √3, where X is the reactance and Z is the impedance.
      - Substituting the values, X = 10% / √3 = 0.1 / √3 = 0.0577.
      - Since the base impedance is given as 30 MVA, we need to scale the reactance accordingly.
      - Scaling factor = (30 MVA / 230 kV)^2 = 130.4348.
      - Scaled reactance = 0.0577 * 130.4348 = 7.5183.
      - Converting to ohms, the final answer is 7.5183 ohms.

      Therefore, the correct answer is option A) 15.87 ohms.

      A 500 MVA, 11KV synchronous generator has 0.2 p.u. synchronous reactance. The p.u. synchronous reactance on the base values of 100 MVA and 22 KV is
      • a)
        0.16
      • b)
        0.01
      • c)
        4.0
      • d)
        0.25
      Correct answer is option 'B'. Can you explain this answer?

      Pooja Patel answered
      Concept:
      The relation between new per-unit value & old per unit value impedance


      Where,
      (Zpu)new = New per unit value of impedance
      (Zpu)old = Old per unit value of impedance
      kVbase = Old base value of voltage
      kVnew = New base value of voltage
      MVAnew = New base value of power
      MVAold = Old base value of power
      Calculation:
      Given that,
      Xd(old) = 0.2 pu
      MVA(new) = 100
      MVA(old) = 500
      KV(old) = 11
      KV(new) = 22

      A 50 Hz synchronous generator is initially connected to a long lossless transmission line which is open circuited at the receiving end. With the field voltage held constant, the generator is disconnected from the transmission line. Which of the following may be said about the steady state terminal voltage and field current of the generator?
      • a)
        The magnitude of terminal voltage decreases, and the field current does not change.
      • b)
        The magnitude of terminal voltage increases, and the field current does not change.
      • c)
        The magnitude of terminal voltage increases, and the field current increases.
      • d)
        The magnitude of terminal voltage does not change and the field current decreases.
      Correct answer is option 'A'. Can you explain this answer?

      A long transmission line under no-load conditions behaves as the capacitive load. The effect of armature current is purely magnetization. When the alternator is disconnected, there is no magnetizing effect. So the terminal voltage decreases with the same field current.
      Explanation:
      When the generator is connected to an open-circuit transmission line, the line draws a charging current, therefore Vt > Eg.

      But, when the generator is disconnected from the line, no charging current is delivered by the generator, i.e.,
      Ic = 0 ⇒ Vt = Eg.
      So, the terminal voltage decreases.

      The reactance of a generator designated ‘x’ is given as 0.25 pu based on the generator’s name plate rating of 18 kV, 500 MVA. If the base for calculations is changed to 20 kV, 100 MVA, the generator reactance X on new base will be - (in pu)
      • a)
        1.025 pu
      • b)
        0.05 pu
      • c)
        0.0405 pu
      • d)
        0.25 pu
      Correct answer is option 'C'. Can you explain this answer?

      Suyash Joshi answered
      By Xg is a measure of its opposition to the flow of alternating current. It is caused by the inductance and capacitance of the generator's windings and is typically expressed in ohms (Ω). The reactance of a generator is frequency-dependent and can be calculated using the formula Xg = 2πfL - 1/(2πfC), where f is the frequency of the alternating current, L is the inductance of the generator's windings, and C is the capacitance of the generator's windings.

      An 11 kV, 25 MVA, 3-phase Y-connected alternator was subjected to three different types of fault at its terminals. The fault currents were:
      5610 A for a three phase fault
      6760 A for line to line fault
      8630 A for single line to ground fault.
      If the alternator neutral is solidly grounded, the zero-sequence reactance of the alternator (in pu) is _________
        Correct answer is between '0.1,0.15'. Can you explain this answer?

        Ameya Gupta answered
        Solution:

        Given data:
        Voltage rating of the alternator (V) = 11 kV
        Apparent power rating of the alternator (S) = 25 MVA
        Fault current for three-phase fault (I3) = 5610 A
        Fault current for line to line fault (I2) = 6760 A
        Fault current for single line to ground fault (I1) = 8630 A
        The alternator neutral is solidly grounded.

        Calculating Zero-sequence Reactance:

        The zero-sequence reactance of the alternator (X0) can be calculated using the following formula:

        X0 = V / (3 * I0)

        where I0 is the zero-sequence current.

        For a three-phase fault, the zero-sequence current is equal to the phase current, i.e., I0 = I3 / √3.

        Substituting the given values in the above formula, we get:

        X0 = 11 kV / (3 * 5610 A / √3) = 0.114 pu

        For a line to line fault, the zero-sequence current is zero, as there is no current flowing through the neutral. Hence, X0 is undefined for this fault.

        For a single line to ground fault, the zero-sequence current is equal to the fault current, i.e., I0 = I1.

        Substituting the given values in the above formula, we get:

        X0 = 11 kV / (3 * 8630 A) = 0.143 pu

        Therefore, the zero-sequence reactance of the alternator is between 0.1 and 0.15 pu, as calculated above.

        Conclusion:

        In conclusion, the zero-sequence reactance of the alternator can be calculated using the formula X0 = V / (3 * I0), where I0 is the zero-sequence current. For a three-phase fault and a single line to ground fault, the zero-sequence current can be calculated using the given fault current values. However, for a line to line fault, the zero-sequence current is zero, and hence, X0 is undefined.

        A 30 kV, 50 Hz, 50 MVA generator has the positive, negative, and zero sequence reactance’s of 0.25 pu, 0.15 pu, and 0.05 pu, respectively. The neutral of the generator is grounded with a reactance so that the fault current for a bolted LG fault and that of a bolted three-phase fault at the generator terminal are equal. The value of grounding reactance in ohms (round off to one decimal 
          Correct answer is between '1.7,1.9'. Can you explain this answer?

          Of X1 = 0.15 pu, X2 = 0.25 pu, and X0 = 0.05 pu, respectively. Calculate the short-circuit current at the generator terminals for a three-phase fault at the generator terminals.

          Solution:

          The short-circuit current can be calculated using the symmetrical component method as follows:

          1) Positive sequence current:

          I1 = 1/3 * MVA / kV / √3 = 50e6 / 30e3 / √3 = 962.25 A

          2) Negative sequence current:

          I2 = K * I1 = 0.25 * 962.25 = 240.56 A

          3) Zero sequence current:

          I0 = K * I1 = 0.05 * 962.25 = 48.11 A

          where K = X2 / X1 = 0.25 / 0.15 = 1.67

          The total short-circuit current is the vector sum of the three components:

          Isc = √(I1^2 + I2^2 + I0^2) = √(962.25^2 + 240.56^2 + 48.11^2) = 996.35 A

          Therefore, the short-circuit current at the generator terminals for a three-phase fault is 996.35 A.

          On a base of 132 kV, 100 MVA, a transmission line has 0.2 per unit impedance. On a base of 220 kV, 50 MVA, it will have a per unit impedance of:
          • a)
          • b)
          • c)
          • d)
          Correct answer is option 'C'. Can you explain this answer?

          Concept:
          Per unit quantity:
          Per unit quantity = Actual quantity in the units / Base (or) reference quantity in the same units
          ⇒ Per unit impedance Zpu = Zactual / Zbase
          ⇒ Zpu = ZΩ × MVAb / (kVb)2
          Conversion of one per unit impedance into another per unit impedance is given by
          Calculation:
          Given that
          Zpu old = 0.2
          MVAold = 100 MVA
          kVb old = 132 kV
          MVAnew = 50 MVA
          kVb new = 220 kV

          The pu parameters for a 300 MVA machine on its own base are inertia M = 10 pu and reactance X = 4 pu. The pu values of inertia and reactance on 50 MVA common base, respectively, will be:
          • a)
            60, 0.67
          • b)
            40, 0.67
          • c)
            60, 0.4
          • d)
            4, 10
          Correct answer is option 'A'. Can you explain this answer?

          Pooja Patel answered
          Given that, pu parameters for a 300 MVA machine on its own base Inertia: Mold = 10 pu
          Reactance: Xold = 4 pu
          New base = 50 MVA
          New pu value of inertia,

          New pu value of reactance,


          Note:
          We know that Pu value depends on the base value of that quantity hence the actual value of that quantity is always equal-
          pu value old = actual/old base
          Now, new pu value = actual/new base
          ⇒ Puold × Base old = Punew × Basenew
          ⇒ pu new = (pu old × old base)/(new base) 

          Open circuit electrical fault is also called as _____
          • a)
            Series fault
          • b)
            Shunt fault
          • c)
            Short circuit fault
          • d)
            Series-Shunt fault
          Correct answer is option 'A'. Can you explain this answer?

          Open circuit electrical fault is also called as Series fault.

          An open circuit electrical fault occurs when there is a break or discontinuity in an electrical circuit, resulting in the interruption of the current flow. This fault is also known as a series fault because it affects the series connection of components in the circuit.

          Causes of Open Circuit Fault:
          - Broken wire: A wire may break due to mechanical stress, corrosion, or accidental damage.
          - Loose connection: If a connection is not properly tightened or secured, it may become loose over time, leading to an open circuit fault.
          - Faulty switch or relay: A malfunctioning switch or relay can cause an open circuit fault when it fails to close the circuit.

          Effects of Open Circuit Fault:
          - Interruption of current flow: An open circuit fault breaks the path of current flow, resulting in no current passing through the circuit.
          - Loss of functionality: As the current is interrupted, the electrical devices connected in the circuit will not function properly or may not work at all.
          - Voltage drop: When an open circuit fault occurs, the voltage across the fault increases substantially. This can cause damage to other components in the circuit due to excessive voltage.

          Identification and Troubleshooting:
          - Visual inspection: A broken wire or loose connection can often be identified through visual inspection of the circuit.
          - Continuity testing: Using a multimeter or continuity tester, the circuit can be checked for continuity. If there is no continuity, it indicates an open circuit fault.
          - Troubleshooting steps: Once the fault is identified, the broken wire can be repaired or replaced. Loose connections can be tightened or secured properly. Faulty switches or relays may need to be replaced.

          Prevention:
          - Proper installation: Ensuring that all connections are properly tightened and secured during installation can help prevent open circuit faults.
          - Regular maintenance: Conducting periodic inspections and maintenance can help identify and rectify any potential open circuit faults before they cause significant issues.
          - Use of protective enclosures: Protecting the electrical circuitry with suitable enclosures can prevent accidental damage to the wires and components.

          In conclusion, an open circuit electrical fault, also known as a series fault, occurs when there is a break or discontinuity in an electrical circuit. It interrupts the current flow, affects the functionality of electrical devices, and can cause voltage drop. Identification and troubleshooting involve visual inspection, continuity testing, and appropriate repairs. Preventive measures include proper installation, regular maintenance, and the use of protective enclosures.

          Chapter doubts & questions for Symmetrical and Unsymmetrical Fault Analysis - 6 Months Preparation for GATE Electrical 2025 is part of Electrical Engineering (EE) exam preparation. The chapters have been prepared according to the Electrical Engineering (EE) exam syllabus. The Chapter doubts & questions, notes, tests & MCQs are made for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, notes, meanings, examples, exercises, MCQs and online tests here.

          Chapter doubts & questions of Symmetrical and Unsymmetrical Fault Analysis - 6 Months Preparation for GATE Electrical in English & Hindi are available as part of Electrical Engineering (EE) exam. Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.

          Top Courses Electrical Engineering (EE)